Originally Posted by
SecondGen
Looking at the specs, your test set is capable of 12mA @ 4kVAC? You only need 1.6kV for the test, if you have the ability to access the equipment for the DMM test, why not just give the Megger test set a shot? If it doesn't work, try your calculation. Just bring up the voltage test really slow and make sure the current doesn't jump too high in the process, I think its worth a shot.
Megger 230425 specs:
Applied Test Voltage 0 to 4 kV, 0 to 5 kVdc
Adjustable Leakage Current Trip Level AC: 0.3 to 12 mA, DC: 0.43 to 17 mA