    480V 2000A Bus - Hipot

    Looking to hipot a run of 480V 2000A busduct, approx 200'. We don't typically hipot LV items. Trying to verify the capacity of the instrument to test the bus. Was going to connect 120V to the bus and meter milliamps using a digital multi meter. I don't know the capacitance of the DUT, and am almost positive that this instrument can't handle - it's a Megger 230425. Planning on using the formula: hipot test voltage (2000VAC )/leakage current test voltage (120VAC) * leakage current (measured in mA using the DMM) to determine the hipot current, and thereby select an instrument. The 2000VAC test voltage is based on the rule of thumb 2x RMS line voltage + 1000. NETA table 100.17 shows 1600VAC max test voltage for Nonsegregated Phase-type bus with a rated kV of 635 - it's the closest thing in the book I could find to the 480 bus that we're dealing with. Any feedback would be greatly appreciated!!

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by jts1976 View Post
    Looking to hipot a run of 480V 2000A busduct, approx 200'. We don't typically hipot LV items. Trying to verify the capacity of the instrument to test the bus. Was going to connect 120V to the bus and meter milliamps using a digital multi meter. I don't know the capacitance of the DUT, and am almost positive that this instrument can't handle - it's a Megger 230425. Planning on using the formula: hipot test voltage (2000VAC )/leakage current test voltage (120VAC) * leakage current (measured in mA using the DMM) to determine the hipot current, and thereby select an instrument. The 2000VAC test voltage is based on the rule of thumb 2x RMS line voltage + 1000. NETA table 100.17 shows 1600VAC max test voltage for Nonsegregated Phase-type bus with a rated kV of 635 - it's the closest thing in the book I could find to the 480 bus that we're dealing with. Any feedback would be greatly appreciated!!
    Looking at the specs, your test set is capable of 12mA @ 4kVAC? You only need 1.6kV for the test, if you have the ability to access the equipment for the DMM test, why not just give the Megger test set a shot? If it doesn't work, try your calculation. Just bring up the voltage test really slow and make sure the current doesn't jump too high in the process, I think its worth a shot.

    Megger 230425 specs:
    Applied Test Voltage 0 to 4 kV, 0 to 5 kVdc
    Adjustable Leakage Current Trip Level AC: 0.3 to 12 mA, DC: 0.43 to 17 mA

  4. #3
  5. Join Date
    Jun 2017
    Location
    USA
    Posts
    11
    Reputation
    Quote Originally Posted by SecondGen View Post
    Looking at the specs, your test set is capable of 12mA @ 4kVAC? You only need 1.6kV for the test, if you have the ability to access the equipment for the DMM test, why not just give the Megger test set a shot? If it doesn't work, try your calculation. Just bring up the voltage test really slow and make sure the current doesn't jump too high in the process, I think its worth a shot.

    Megger 230425 specs:
    Applied Test Voltage 0 to 4 kV, 0 to 5 kVdc
    Adjustable Leakage Current Trip Level AC: 0.3 to 12 mA, DC: 0.43 to 17 mA

    Thanks SecondGen. We'll be onsite tomorrow, and will megger to make sure we're getting a good reading before hipot testing. Standard insulation resistance readings from GE for LV spectra series bus is 1 Mega ohm/100' (run is approx 200'). Here's what I got from GE today:

    The test parameters should be 1000vdc (phase to phase and phase to ground). When conducting, this test ensure the Busway has NO connection or contact with any potential power source.
    The standard for megger readings for all busway manufactured in the US is one (1) megohm per 100 ft. The required minimum reading per 100 ft. is published In NEMA Standard BU1.1 and published by GE in the Spectra Series™ busway Installation Instruction DEH-40087.

    I think we'll take your advice and hit it with the 230425 to see what happens. . .

Subscribe

Share this thread

Related Topics

  1. Should I HIPOT before or after other tests?
    By DJ-Jokes in forum Electrical Testing Talk
    Replies: 12
    Last Post: December 3, 2021, 02:10 PM
  2. VLF vs AC HiPot
    By Kalbi_Rob in forum Electrical Testing Talk
    Replies: 13
    Last Post: May 4, 2021, 05:44 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net