    5,000A Magnum SB Ground Fault verification

    Does anyone have experience doing a Ground Fault verification through a neutral CT on a 5,000A Magnum SB main Breaker with a Digitrip 520 trip unit?

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by MrBolt View Post
    Does anyone have experience doing a Ground Fault verification through a neutral CT on a 5,000A Magnum SB main Breaker with a Digitrip 520 trip unit?
    Fairly standard breaker and test, what is the issue?

  4. #3
  5. MrBolt is offline Junior Member Pro Subscriber
    Join Date
    Oct 2018
    Posts
    8
    Reputation
    Quote Originally Posted by SecondGen View Post
    Fairly standard breaker and test, what is the issue?
    ground fault setting is 1200A max.
    I dialed it down to 0.25, and Delay @ 0.5 - but it kept tripping at 700A. I just don't understand why.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by MrBolt View Post
    ground fault setting is 1200A max.
    I dialed it down to 0.25, and Delay @ 0.5 - but it kept tripping at 700A. I just don't understand why.
    What size sensors and plug? Assuming 5000/5000, a GF setting of 0.25x should still be 1200A like you stated. What is the test setup, are you pushing current straight across the neutral CT in a switchboard? What are your phase LTPU values when ground fault is disabled?

  8. #5
  9. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by MrBolt View Post
    ground fault setting is 1200A max.
    I dialed it down to 0.25, and Delay @ 0.5 - but it kept tripping at 700A. I just don't understand why.
    Depending on your test setup, you may be getting a half trip if your polarities are backwards. The 0.5 time delay would allow for a little extra current over the expected 600A half trip.

  10. #6
  11. MrBolt is offline Junior Member Pro Subscriber
    Join Date
    Oct 2018
    Posts
    8
    Reputation
    Quote Originally Posted by SecondGen View Post
    What size sensors and plug? Assuming 5000/5000, a GF setting of 0.25x should still be 1200A like you stated. What is the test setup, are you pushing current straight across the neutral CT in a switchboard? What are your phase LTPU values when ground fault is disabled?
    yes 5,000A plug. pushing current from Line side of A phase, Jumper From load side of A phase to Neutral CT, and other side of CT - back to test set.
    my question is, Shouldn't 1200*0.25=300A?
    and shouldn't it trip @ 50% its current setting?

  12. #7
  13. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by MrBolt View Post
    yes 5,000A plug. pushing current from Line side of A phase, Jumper From load side of A phase to Neutral CT, and other side of CT - back to test set.
    my question is, Shouldn't 1200*0.25=300A?
    and shouldn't it trip @ 50% its current setting?
    Typically ground fault settings are based off the sensor, in this case assuming 5000A would be 5000 * 0.25 = 1250A. Since 1200A is max, the trip unit will default to 1200A. My guess is that you are getting a half trip, try reversing the direction of current through the neutral CT. If that fixes the problem, verify that the CT is facing the proper direction per design drawings.

  14. #8
  15. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Below is the link to the Digitrip 520 manual.

    https://docs.natlswgr.com/docs/W1000028.pdf

    If you notice the table on page 12, for a 5000A breaker, all ground fault settings place the trip at 1200A maximum per NEC. Thus the GF trip setting is not adjustable on such a large breaker. As described above, it sounds like your CT is reversed. No trip test is placing test set leads on the line side of the breaker phase, and Neutral Ct, and the jumper across the load side phase of the breaker and Neutral CT. 50% trip test would be reversing the leads across the neutral CT. For visual reference see the below link.

    https://testguy.net/content/279-Grou...Testing-Basics

  16. #9
  17. MrBolt is offline Junior Member Pro Subscriber
    Join Date
    Oct 2018
    Posts
    8
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Below is the link to the Digitrip 520 manual.

    https://docs.natlswgr.com/docs/W1000028.pdf

    If you notice the table on page 12, for a 5000A breaker, all ground fault settings place the trip at 1200A maximum per NEC. Thus the GF trip setting is not adjustable on such a large breaker. As described above, it sounds like your CT is reversed. No trip test is placing test set leads on the line side of the breaker phase, and Neutral Ct, and the jumper across the load side phase of the breaker and Neutral CT. 50% trip test would be reversing the leads across the neutral CT. For visual reference see the below link.

    https://testguy.net/content/279-Grou...Testing-Basics
    Thanks for the information, I didn't understand why the breaker was tripping around 600A. now it makes sense if the GF is not adjustable.

Subscribe

Share this thread

Related Topics

  1. Ground fault trips at half of setting
    By joenavymctest in forum P&C / Relay Testing Talk
    Replies: 6
    Last Post: March 6, 2020, 08:45 AM
  2. Zone ground fault protection. Blocking and tripping?
    By marvinray in forum NETA Level 4 Exam
    Replies: 3
    Last Post: October 6, 2017, 03:42 PM
  3. Testing ground fault reduced voltage and blocking capability
    By Sanjayo in forum Electrical Testing Talk
    Replies: 5
    Last Post: January 29, 2016, 02:46 PM
  4. What is ground fault blocking capability?
    By madsenate in forum NETA Level 3 Exam
    Replies: 2
    Last Post: June 23, 2015, 11:03 AM
  5. Ground fault explained with simple light circuit
    By CCooter in forum NETA Level 2 Exam
    Replies: 0
    Last Post: May 5, 2015, 09:56 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net