Does anyone have experience doing a Ground Fault verification through a neutral CT on a 5,000A Magnum SB main Breaker with a Digitrip 520 trip unit?
Does anyone have experience doing a Ground Fault verification through a neutral CT on a 5,000A Magnum SB main Breaker with a Digitrip 520 trip unit?
Typically ground fault settings are based off the sensor, in this case assuming 5000A would be 5000 * 0.25 = 1250A. Since 1200A is max, the trip unit will default to 1200A. My guess is that you are getting a half trip, try reversing the direction of current through the neutral CT. If that fixes the problem, verify that the CT is facing the proper direction per design drawings.
Below is the link to the Digitrip 520 manual.
https://docs.natlswgr.com/docs/W1000028.pdf
If you notice the table on page 12, for a 5000A breaker, all ground fault settings place the trip at 1200A maximum per NEC. Thus the GF trip setting is not adjustable on such a large breaker. As described above, it sounds like your CT is reversed. No trip test is placing test set leads on the line side of the breaker phase, and Neutral Ct, and the jumper across the load side phase of the breaker and Neutral CT. 50% trip test would be reversing the leads across the neutral CT. For visual reference see the below link.
https://testguy.net/content/279-Grou...Testing-Basics