how do you demagnetize a transformer?
how do you demagnetize a transformer?
AC or DC can be used. AC amps applied close to the excitation knee and slowly lowered can demag, and long tedious alternating of lowering DC currents can demag. Edit: I would highly recommend using AC
Previous TestGuy thread about it:
https://testguy.net/threads/2749-Cor...nsformer-cores
Article on importance of demag xfmrs with AC explanation:
https://www.tdworld.com/substations/...nsformer-cores
More like alternating DC, which is effectively AC - just not the 60Hz frequency you might be used to. You can use a car battery to pass current thru a winding in different directions, if you watch a winding resistance test set de-mag function you can see the process in action.
An example would be something like this:
+10A
-10A
+7A
-7A
+5A
-5A
+3A
-3A
+1A
-1A
This isn't exact by any means, I'm just trying to show an example. I'm sure you can also use regular AC voltage but a car battery was mentioned earlier and that's how I was originally taught. Also winding resistance sets usually operate off DC which is why the above method is used. As far as I understand you only need to perform this on one winding to de-mag a polyphase transformer.