    #1
  1. dukeofsmooth is offline
    WAR EAGLE!
    Junior Member Pro Subscriber
    Join Date
    Sep 2016
    Location
    Allentown, PA
    Posts
    8
    Reputation

    CT Apparent Burden Problem

    A watt-hour meter draws 1.5 watts and 11.3 Vars from a potential transformer, and 1.88 watts and 1.8 Vars from a current transformer, the total apparent burden placed on the current transformer is?

    Explain the concept of this "apparent burden" problem.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by dukeofsmooth View Post
    A watt-hour meter draws 1.5 watts and 11.3 Vars from a potential transformer, and 1.88 watts and 1.8 Vars from a current transformer, the total apparent burden placed on the current transformer is?

    Explain the concept of this "apparent burden" problem.
    Burden is shown as apparent power (S or VA). Thus to calculate the total apparent burden placed on just the CT, we need to convert watts and vars to VA.
    S^2=P^2+Q^2
    S=sqrt((1.88 Watts)^2+(1.8 Vars)^2) = 2.603 VA

    That's my best guess at the answer, seems to simple to be right though.

  4. #3
  5. dukeofsmooth is offline
    WAR EAGLE!
    Junior Member Pro Subscriber
    Join Date
    Sep 2016
    Location
    Allentown, PA
    Posts
    8
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Burden is shown as apparent power (S or VA). Thus to calculate the total apparent burden placed on just the CT, we need to convert watts and vars to VA.
    S^2=P^2+Q^2
    S=sqrt((1.88 Watts)^2+(1.8 Vars)^2) = 2.603 VA

    That's my best guess at the answer, seems to simple to be right though.
    You used the "Power Triangle" in concert with the Pythagorean theorem to solve! Great stuff! I did not see or thinkof that for whatever.

Subscribe

Share this thread

Related Topics

  1. Problem running ratio test with Megger multitap CT test set
    By ejbrewer in forum Electrical Testing Talk
    Replies: 5
    Last Post: June 30, 2016, 03:13 AM
  2. Total burden on current transformer
    By Sanjayo in forum NETA Level 3 Exam
    Replies: 1
    Last Post: February 19, 2016, 01:50 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net