    How much is the alternator phase current?

    I have been stuck on this question and just can't seem to figure out how to get the correct answer of 6.93.

    Would you be able to show the work needed for this?

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by clayton View Post
    I have been stuck on this question and just can't seem to figure out how to get the correct answer of 6.93.

    Would you be able to show the work needed for this?
    Can you assist us by stating the question you need answering?

  4. #3
  5. clayton is offline Junior Member Pro Subscriber
    Join Date
    Feb 2019
    Posts
    2
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Can you assist us by stating the question you need answering?
    Ahh, well wouldn't that make a whole lot of sense. I guess I assumed people could read my mind

    A wye-connected alternator that has phase voltages of 277 V is feeding two loads. The first load is wye-connected inductors that have 40 ohms of XL. The second load is a set of delta-connected capacitors that have XC of 60 ohms. How much is the alternator phase current?

  6. #4
  7. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by clayton View Post
    Ahh, well wouldn't that make a whole lot of sense. I guess I assumed people could read my mind

    A wye-connected alternator that has phase voltages of 277 V is feeding two loads. The first load is wye-connected inductors that have 40 ohms of XL. The second load is a set of delta-connected capacitors that have XC of 60 ohms. How much is the alternator phase current?
    I can't help you, I only get 20.781 A. Now the current flowing through the Wye-connected inductors appears to be 6.93A. I have to ask if you might have misunderstood the question.

  8. #5
  9. J2019L is offline Junior Member Pro Subscriber
    Join Date
    May 2014
    Location
    Seattle, WA
    Posts
    7
    Reputation
    Quote Originally Posted by clayton View Post
    I have been stuck on this question and just can't seem to figure out how to get the correct answer of 6.93.

    Would you be able to show the work needed for this?
    1. Convert Xc from delta connection to Y connection. In Y connection, Xc'= 60*60/(60+60+60)=20
    2. Calculate balance 3-phase circuit for two loads, parallel Xc' & XL. Total load 1/X= (1-2)j/40 --> X=40j (reactance)

    3. 3-Phase balance current I = 277/40 = 6.925 --Ans

  10. #6
  11. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Jimmy Lee View Post
    1. Convert Xc from delta connection to Y connection. In Y connection, Xc'= 60*60/(60+60+60)=20
    2. Calculate balance 3-phase circuit for two loads, parallel Xc' & XL. Total load 1/X= (1-2)j/40 --> X=40j (reactance)

    3. 3-Phase balance current I = 277/40 = 6.925 --Ans
    Aww, that's the equation I forgot

    Z=1/(sqrt((1/R)^2+((1/XL)-(1/XC))^2))

    Click image for larger version. 

Name:	Untitled.png 
Views:	13 
Size:	4.2 KB 
ID:	334

  12. #7
  13. J2019L is offline Junior Member Pro Subscriber
    Join Date
    May 2014
    Location
    Seattle, WA
    Posts
    7
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Aww, that's the equation I forgot

    Z=1/(sqrt((1/R)^2+((1/XL)-(1/XC))^2))

    Click image for larger version. 

Name:	Untitled.png 
Views:	13 
Size:	4.2 KB 
ID:	334
    To solve this question, need to have math and electric concept. In the complex number, R represents real part and Xc, XL represent complex parts. So, R is the number on the real axis and Xc and XL are the number on the complex axis. Xc and XL are the number on complex axis, but XL is positive (to up side) Xc is negative (to down side) on the complex axis. Therefore, it is showed minus between (1/XL -1/Xc). And in this question R = 0, The equation becomes simplified Z = 1/sqrt((1/XL)-(1/XC))^2)

Subscribe

Share this thread

Related Topics

  1. alternator frequency????
    By lester mcmanaway in forum NETA Level 3 Exam
    Replies: 7
    Last Post: February 1, 2019, 12:05 AM
  2. 1 phase AC 115V 1 HP motor full load current calc.
    By davidb in forum NETA Level 2 Exam
    Replies: 0
    Last Post: May 2, 2018, 02:13 PM
  3. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 11:14 AM
  4. Help understanding 3 phase electrical systems
    By randywright in forum Electrical Testing Talk
    Replies: 5
    Last Post: October 22, 2015, 11:46 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net