Load currents in an alternator

 Jump to latest post
    #1
  1. JeremyBrown87 is offline
    Lord of the Lightning
    Junior Member Pro Subscriber
    Join Date
    Nov 2018
    Location
    Taftville, CT
    Posts
    4
    Reputation

    Load currents in an alternator

    16. A wye-connected alternator that has phase voltages of 277 V is feeding two loads. The first load is wye-connected inductors that have 40 ohms of XL. The second load is a set of delta-connected capacitors that have XC of 60 ohms. How much is the alternator phase current?
    Your Answer: 14.93 A
    Correct Answer: 6.93 A

    So I didn't realized that the One load was Wye and other was delta, how does this change the total Z eqn? I tried to answer in a couple ways but couldn't come up with correct answer

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by JeremyBrown87 View Post
    16. A wye-connected alternator that has phase voltages of 277 V is feeding two loads. The first load is wye-connected inductors that have 40 ohms of XL. The second load is a set of delta-connected capacitors that have XC of 60 ohms. How much is the alternator phase current?
    Your Answer: 14.93 A
    Correct Answer: 6.93 A

    So I didn't realized that the One load was Wye and other was delta, how does this change the total Z eqn? I tried to answer in a couple ways but couldn't come up with correct answer
    See previous thread on this question:

    https://testguy.net/threads/5955-How...-phase-current

  4. #3
  5. JeremyBrown87 is offline
    Lord of the Lightning
    Junior Member Pro Subscriber
    Join Date
    Nov 2018
    Location
    Taftville, CT
    Posts
    4
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    See previous thread on this question:

    https://testguy.net/threads/5955-How...-phase-current
    Thanks! Unfortunately still not able to figure it out.

  6. #4
  7. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by JeremyBrown87 View Post
    Thanks! Unfortunately still not able to figure it out.
    So first you want to convert Xc Delta connected load to Xc Wye load(simplify the math): Xc(Wye)=(Xa*Xb)/(Xa+Xb+Xc)=(60*60)/(60+60+60)=20 (this is just a single phase version of all three equations to be simplified, see https://www.allaboutcircuits.com/tex...y-conversions/).

    Next, you have to add two reactances in parallel: Z=1/(sqrt((1/R)^2+((1/XL)-(1/XC))^2)), where R=0 thus Z=1/(sqrt((1/0)^2+((1/40)-(1/20))^2))=40
    Taken from Impedance of a Parallel RLC Circuit found on this website: https://www.electronics-tutorials.ws...l-circuit.html

    Then calculate the current of the alternator knowing that current is equal on a Wye connection between phase and line, I=277/40=6.93A

    There is another much more difficult (easier math but higher level) way to calculate this using rectangular formulas and Siemens using Laplace equations.

Subscribe

Share this thread

Related Topics

  1. How much is the alternator phase current?
    By clayton in forum NETA Level 3 Exam
    Replies: 6
    Last Post: March 21, 2019, 05:35 PM
  2. alternator frequency????
    By lester mcmanaway in forum NETA Level 3 Exam
    Replies: 7
    Last Post: February 1, 2019, 12:05 AM
  3. 1 phase AC 115V 1 HP motor full load current calc.
    By davidb in forum NETA Level 2 Exam
    Replies: 0
    Last Post: May 2, 2018, 02:13 PM
  4. How to locate harmonic currents?
    By AlexT90 in forum Electrical Testing Talk
    Replies: 2
    Last Post: June 14, 2017, 10:50 AM
  5. Testing liquid filled transformers with load break bushings
    By GDerr81 in forum Electrical Testing Talk
    Replies: 2
    Last Post: November 15, 2016, 02:47 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net