Totally misunderstood you. I have no experience with RL breakers but we did do some SACE breakers last year with one of these adjustable stab sets, which worked great:
http://www.newengland-tool.com/id22.html. But they were 3200A and the time dial was not all the way up. At 144s and 5000A the LTD test would be 15000A for about 2.5 minutes! That is some serious current and a PI-6000 would have trouble pushing that according to the spec sheet (max on time for 18kA @ 9V = 1.5 mins).
I did not know that! I was taught to start just below the low tolerance, then inject higher and higher until the breaker trips, and then the trip current is the test result. What you/NEMA says makes sense, it's similar to how we test relays where they want to prove both sides of a tolerance. Thanks for the info, I guess I need to read the NEMA book some more.