Originally Posted by
test11
I would absolutely recommend a dial down. Some customers don't like the idea of testing differently from study. However, you're beating the hell out of their equipment most of the time. It's not in the cubicle to help with the shock and you're definitely wearing out the contacts. You're testing if the breaker will function properly, not doing a current withstand test for UL listing.
I've also seen breakers on skateboards(like a funiture dolly) jump out of test stabs at higher currents due to forces produced. So you could argue personnel safety as well.
Bring these up to the customer when they object and usually they come around.
One thing to note is that you should really pickup a manual for the particular trip unit. For example, I know some Eaton trip units have an instantaneous override making it impossible to test high settings in the field.