Warrengarber
I have a question about interpreting the DLRO results. According to the NETA MTS 2019, 7.6.1.2 Circuit Breakers, Air, Low-Voltage Power, D. Test Values – Electrical, #3 "Microhm or dc millivolt drop values should not exceed the high levels of the normal range as indicated in the manufacturer’s published data. If manufacturer’s data is not available, investigate values that deviate from adjacent poles or similar breakers by more than 50
percent of the lowest value." Both the LV Air Switch and Molded Case Circuit breaker use this wording. When they refer to adjacent poles. I would read that as comparing A phase to B phase and B phase to C phase but not A phase to C phase.
Example: 151(A), 128(B), 98(C). 50% of lowest reading (98) would be 98/2=49. So phase A (151) is within 49 ohms of adjacent pole B (128), and phase B (128) is within 49 ohms of adjacent pole C (98). Phase A (151) is NOT within 50% (49 ohms) of phase C (98). A and C phases are not adjacent to one another in my mind.
Would these reading be acceptable? Are we supposed to also compare A phase to C phase? There have been questions similar to this on every test I have taken and I want to make sure that this simple question is not one that I am missing. Thanks for any input.