    Would the current injection, during a substation grounding study, operate any relaying?

    I’m having a study performed on several substations soon and I am concerned that there may be some type of trip or alarms due to the current injection during the study.

  2. #2
  3. Warrengarber's Avatar
    Warrengarber is offline
    If you ignore it, it will fail.
    Seasoned Member
    Join Date
    Jul 2017
    Location
    Jacksonville, FL
    Posts
    62
    Reputation
    Quote Originally Posted by Eazyeet View Post
    Would the current injection, during a substation grounding study, operate any relaying?

    I’m having a study performed on several substations soon and I am concerned that there may be some type of trip or alarms due to the current injection during the study.
    What type of ground testing are you going to be doing?

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Eazyeet View Post
    Would the current injection, during a substation grounding study, operate any relaying?

    I’m having a study performed on several substations soon and I am concerned that there may be some type of trip or alarms due to the current injection during the study.
    In my opinion, it's possible you could trip something depending on the protection scheme and test procedure. All it takes is enough current passing through a ground CT to trigger a pickup or imbalance.

    There have been numerous incidents where using a DLRO on switchgear bus has caused a relay to trip. I'd be extra cautious.

  6. #4
  7. Relay1's Avatar
    Relay1 is offline
    I use to be disgusted, now I'm just amused!
    Junior Member
    Join Date
    Nov 2017
    Location
    Central Texas
    Posts
    17
    Reputation

    Ground Study

    Quote Originally Posted by Eazyeet View Post
    Would the current injection, during a substation grounding study, operate any relaying?

    I’m having a study performed on several substations soon and I am concerned that there may be some type of trip or alarms due to the current injection during the study.
    Depending on what type of equipment you are using to inject current, the chance of operating a relay are very slim. If it is a DC unit, the current flows from one lead to the ground grid and back to its source. It would have no affect on a CT in its return path. If it is an AC unit, current also flows from one lead to the ground grid and back to its source. There are a lot of paths it may take but the impedance of a power transformer should be enough to block that direction of current flow through the neutral.

  8. #5
  9. Warrengarber's Avatar
    Warrengarber is offline
    If you ignore it, it will fail.
    Seasoned Member
    Join Date
    Jul 2017
    Location
    Jacksonville, FL
    Posts
    62
    Reputation
    Quote Originally Posted by Eazyeet View Post
    Would the current injection, during a substation grounding study, operate any relaying?

    I’m having a study performed on several substations soon and I am concerned that there may be some type of trip or alarms due to the current injection during the study.
    I agree a with Secondgen and would exercise extreme caution. If you contact the test set manufacture and explain the scope of the testing they should be able to get you the information that they need. If you are doing a three point fall of potential test I would think you would be ok but with the two point direct method the DLRO is actually using the circuit as a path for voltage and current probe to probe, very small but it is still there, and it could cause an issue.