Follow Us
Page 2 of 2 FirstFirst 12
Results 11 to 16 of 16

NETA III Test April 2019

 Jump to latest post
Page 2 of 2 FirstFirst 12
    #11
  1. rofo42 is offline Seasoned Member
    Join Date
    Apr 2018
    Posts
    65
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    You just put all the resistances in parallel between the end 15 ohm resistances. They are in series on the parallel bus bars.

    R= 15+(1/((1/(5+10+5)+(1/(5+10+5)))+15 = 15+(1/((1/20)+(1/20)))+15 = 15+10+15 = 40

    Don't quote me on this being the right answer, but that's how I see it.
    That is how I see it also. This question was also on my level II test.

    This is how I visualize it.
    Click image for larger version. 

Name:	Total-resistance.jpg 
Views:	17 
Size:	60.0 KB 
ID:	417

  2. #12
  3. jfoster is offline Junior Member Pro Subscriber
    Join Date
    Mar 2015
    Posts
    11
    Reputation
    Quote Originally Posted by rofo42 View Post
    That is how I see it also. This question was also on my level II test.

    This is how I visualize it.
    Click image for larger version. 

Name:	Total-resistance.jpg 
Views:	17 
Size:	60.0 KB 
ID:	417
    Thank you

  4. #13
  5. clipboardwarrior's Avatar
    clipboardwarrior is offline Junior Member Pro Subscriber
    Join Date
    Mar 2018
    Posts
    13
    Reputation
    Quote Originally Posted by SecondGen View Post
    Easy way to calculate:
    A2 + B2 = C2

    750,000 = C2
    750,000 x 0.95 = 712,500 = A2
    750,000 - 712,500 = 37,500 = B2
    sqrt(37,500) = 193.64
    I agree with most of this. Until you came up with B2.

    sqrt(750,000sq - 712,500sq) = 234.42 = B2

    Thoughts? I know this is an old post, but, for those of us studying, it's still relevant.

  6. #14
  7. jgraves is offline Junior Member Pro Subscriber
    Join Date
    Jan 2018
    Posts
    6
    Reputation
    Quote Originally Posted by clipboardwarrior View Post
    I agree with most of this. Until you came up with B2.

    sqrt(750,000sq - 712,500sq) = 234.42 = B2

    Thoughts? I know this is an old post, but, for those of us studying, it's still relevant.
    I don't think A^2+B^=C^2 method is the right way to go about the problem. Kw loading will stay the same, but changing the kvar will cause the kva to change.

    Page 4 of (https://www.eaton.com/ecm/groups/pub...a02607001e.pdf) has a good visual of the change.

    The OP's method seems the quickest to answer the problem:
    1. Solve for kw. (pf x KVAinitial =kw) --- 0.75 x 750000 = 562500 Kw
    2. Find the angle for .95 pf. (cos-1 [Pfdesired]= angle) --- cos-1 (0.95) = 18.19 degrees
    3. Solve for Kvar. (tan[angle] x kw = kvar) --- tan(18.19) x 562500 = 184831 Kvar


    For fun you can then use A^2+B^=C^2 to solve for the new Kvar = 592088 Kvar

  8. #15
  9. clipboardwarrior's Avatar
    clipboardwarrior is offline Junior Member Pro Subscriber
    Join Date
    Mar 2018
    Posts
    13
    Reputation
    Quote Originally Posted by jgraves View Post
    I don't think A^2+B^=C^2 method is the right way to go about the problem. Kw loading will stay the same, but changing the kvar will cause the kva to change.

    Page 4 of (https://www.eaton.com/ecm/groups/pub...a02607001e.pdf) has a good visual of the change.

    The OP's method seems the quickest to answer the problem:
    1. Solve for kw. (pf x KVAinitial =kw) --- 0.75 x 750000 = 562500 Kw
    2. Find the angle for .95 pf. (cos-1 [Pfdesired]= angle) --- cos-1 (0.95) = 18.19 degrees
    3. Solve for Kvar. (tan[angle] x kw = kvar) --- tan(18.19) x 562500 = 184831 Kvar


    For fun you can then use A^2+B^=C^2 to solve for the new Kvar = 592088 Kvar
    You're absolutely right. Between the time I read the OP and then read the follow up comment, I spaced on the VA changing! Yoinks! Hopefully, I don't pull any dumb stunts like that next week when I take my test.

  10. #16
  11. jaycee91 is offline Junior Member Pro Subscriber
    Join Date
    Dec 2016
    Posts
    4
    Reputation
    63.) What is a newer SCADA system that doesn’t require cables?
    a. HMI
    b. RS485
    c. Goose
    d. ?

    correct answer is PLCC so D

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. NETA III TEST Jan 2019
    By cbrazzil in forum NETA Level 3 Exam
    Replies: 2
    Last Post: March 1, 2021, 10:35 AM
  2. Practice Exam Upgrades Summer 2019
    By testguy in forum News and Announcements
    Replies: 3
    Last Post: July 17, 2019, 04:16 PM
  3. Who Else is Taking Level 4 in January 2019?
    By Wanderer20001us in forum NETA Level 4 Exam
    Replies: 0
    Last Post: December 26, 2018, 12:51 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net