    Transformer power factor under vacuum

    What effect, if any, does negative tank pressure have on transformer power factor? I've never known of it being an issue but another tech on site seems to remember hearing it in a PF seminar. Thoughts??

  2. #2
  3. Jrmcritical's Avatar
    Jrmcritical is offline
    NICET Level I (ID: 150100)
    NICET Level 1 Pro Subscriber
    Join Date
    Dec 2018
    Location
    West Fulton, NY
    Posts
    15
    Reputation
    Quote Originally Posted by SecondGen View Post
    What effect, if any, does negative tank pressure have on transformer power factor? I've never known of it being an issue but another tech on site seems to remember hearing it in a PF seminar. Thoughts??
    In theory, it 'shouldn't' have any effect on power factor as power factor is simply a capacitance measurement. With that said, under no circumstances should this test ever be performed under vacuum, as it can greatly (and gravely) increase the chances of flashover.

    I've attached Megger's "Application Guide for Power Factor Testing of Power And Distribution Transformers." It's a great reference and explains a bit more in depth about the relation of pressure vs. vacuum and it's associated hazard.
    Transformers_AG_en_V01.PDF

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Jrmcritical View Post
    In theory, it 'shouldn't' have any effect on power factor as power factor is simply a capacitance measurement. With that said, under no circumstances should this test ever be performed under vacuum, as it can greatly (and gravely) increase the chances of flashover.

    I've attached Megger's "Application Guide for Power Factor Testing of Power And Distribution Transformers." It's a great reference and explains a bit more in depth about the relation of pressure vs. vacuum and it's associated hazard.
    Transformers_AG_en_V01.PDF
    Excellent document, thanks for this. Screenshot below for those interested.

    Click image for larger version. 

Name:	20190522_114626.jpg 
Views:	4 
Size:	959.6 KB 
ID:	367

  6. #4
  7. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by SecondGen View Post
    Excellent document, thanks for this. Screenshot below for those interested.

    Click image for larger version. 

Name:	20190522_114626.jpg 
Views:	4 
Size:	959.6 KB 
ID:	367
    And this always brings up a question that I've never could answer.

    If flashover happens in transformers under vacuum, why is this different than a vacuum circuit breaker? As the salient feature of vacuum as an arc quenching medium is that as soon as the arc is produced in a vacuum, it is quickly extinguished due to the fast rate of recovery of the dielectric strength in vacuum. I realize the medium of an oil filled transformer is different than a vacuum CB, but it always brings up the question. Obviously, all manuals point to never testing under vacuum.

    But then again it might be the DC component that is the problem/cause.

  8. #5
  9. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    And this always brings up a question that I've never could answer.

    If flashover happens in transformers under vacuum, why is this different than a vacuum circuit breaker? As the salient feature of vacuum as an arc quenching medium is that as soon as the arc is produced in a vacuum, it is quickly extinguished due to the fast rate of recovery of the dielectric strength in vacuum. I realize the medium of an oil filled transformer is different than a vacuum CB, but it always brings up the question. Obviously, all manuals point to never testing under vacuum.

    But then again it might be the DC component that is the problem/cause.
    I asked the exact same question to the crew today. Only thing I could think of is that the vacuum pressure is much, much greater in a bottle than a transformer.

    Now what I wonder is: if a flashover can occur at 250V when testing under vacuum, why doesn't it occur at 35kV in normal operation when the transformer is under vacuum?

  10. #6
  11. Jrmcritical's Avatar
    Jrmcritical is offline
    NICET Level I (ID: 150100)
    NICET Level 1 Pro Subscriber
    Join Date
    Dec 2018
    Location
    West Fulton, NY
    Posts
    15
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    And this always brings up a question that I've never could answer.

    If flashover happens in transformers under vacuum, why is this different than a vacuum circuit breaker? As the salient feature of vacuum as an arc quenching medium is that as soon as the arc is produced in a vacuum, it is quickly extinguished due to the fast rate of recovery of the dielectric strength in vacuum. I realize the medium of an oil filled transformer is different than a vacuum CB, but it always brings up the question. Obviously, all manuals point to never testing under vacuum.

    But then again it might be the DC component that is the problem/cause.
    I like where you're going with the possibility of DC current being the reason for a heightened risk of flashover, and thinking about it more in depth it makes sense. For example, think of any capacitor. It allows you to "Store" DC current. So, let's take a power factor test to its most basic form - an insulation resistance test. As were turning a conductor into a capacitor eventually it will reach saturation. If voltage is high enough, similar to a Leyden jar we'd have a flashover. This isn't possible with AC power as it can't be stored (although it can be obtained from stored DC current).

    When looking at a flashover with AC current it's not because of stored energy (as AC current can't be stored) its due to an arc either because of a short circuit, switching under load, or breakdown of insulation (which is basically the same as a short circuit)

  12. #7
  13. Join Date
    Jun 2019
    Posts
    1
    Reputation

    Food for Thought

    Quote Originally Posted by SecondGen View Post
    I asked the exact same question to the crew today. Only thing I could think of is that the vacuum pressure is much, much greater in a bottle than a transformer.

    Now what I wonder is: if a flashover can occur at 250V when testing under vacuum, why doesn't it occur at 35kV in normal operation when the transformer is under vacuum?
    Maybe it's not so much the medium but what may be in the medium?

    Water boils at room temp under vacuum and a vacuum may lift moister in to something it shouldn't be around?

    Let me know if I'm on to something here..

  14. #8
  15. Join Date
    Apr 2018
    Location
    Michigan
    Posts
    40
    Reputation
    Quote Originally Posted by Hireup View Post
    Maybe it's not so much the medium but what may be in the medium?

    Water boils at room temp under vacuum and a vacuum may lift moister in to something it shouldn't be around?

    Let me know if I'm on to something here..
    It appears to be a characteristic of Nitrogen/Helium (maybe all gases). There looks to be a low breakdown point at partial vacuum that would explain the issue. Breakdown voltage continues to lower from atmospheric to a low point prior to increasing again when approaching perfect vacuum (ie vacuum bottles).
    Attached Thumbnails Attached Thumbnails 2-Figure1-1.png  


  16. #9
  17. NBatson's Avatar
    NBatson is offline
    I NETA BREAK
    Junior Member
    Join Date
    Feb 2019
    Location
    TX Gulf Coast
    Posts
    19
    Reputation

    oil or no oil???

    Quote Originally Posted by SecondGen View Post
    What effect, if any, does negative tank pressure have on transformer power factor? I've never known of it being an issue but another tech on site seems to remember hearing it in a PF seminar. Thoughts??



    Is the transformer empty and under vacuum? If so then cancel your plans to do any testing. If its full of oil and just reading negative pressure on the gauge then carry on. Hopefully this isn't a here's your sign episode and I'm not just stating the known.

  18. #10
  19. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by NBatson View Post
    Is the transformer empty and under vacuum? If so then cancel your plans to do any testing. If its full of oil and just reading negative pressure on the gauge then carry on. Hopefully this isn't a here's your sign episode and I'm not just stating the known.
    Power factor testing an empty liquid-filled transformer?

    Click image for larger version. 

Name:	hqdefault.jpg 
Views:	63 
Size:	14.1 KB 
ID:	383

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. Transformer Oil Pressure when Power Factor Testing
    By ElectricalTestTech in forum Electrical Testing Talk
    Replies: 8
    Last Post: October 3, 2020, 09:41 AM
  2. Power Factor for New Mineral Oil
    By Salcama in forum NETA Level 3 Exam
    Replies: 4
    Last Post: February 22, 2020, 05:12 PM
  3. Power factor testing mode of operation
    By E-DivMafia in forum NETA Level 2 Exam
    Replies: 1
    Last Post: October 31, 2018, 02:22 PM
  4. Replies: 9
    Last Post: August 16, 2018, 02:28 PM
  5. Tan / Delta or Power Factor Testing of Dry Type Transformer
    By mask12900 in forum Electrical Testing Talk
    Replies: 1
    Last Post: January 1, 2018, 08:41 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net