    Open delta high leg identification requirement

    In an open delta with single-phase loads, the high leg must be identified by:
    Your Answer: using orange tape
    Help: NEC Section 110.15

    This was marked incorrect, but I do not understand how this is wrong after reviewing the NEC Section 110.15 It tells you to mark the high leg as orange.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Spanky123 View Post
    In an open delta with single-phase loads, the high leg must be identified by:
    Your Answer: using orange tape
    Help: NEC Section 110.15

    This was marked incorrect, but I do not understand how this is wrong after reviewing the NEC Section 110.15 It tells you to mark the high leg as orange.
    After reading NEC 110.15, it seems like the question is not accurate, as it talks about a 4 wire Delta system in which one winding is grounded in the middle and a neutral is landed at that point. This would not be an open delta system as Open delta is a 3 wire system with B phase grounded.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    After reading NEC 110.15, it seems like the question is not accurate, as it talks about a 4 wire Delta system in which one winding is grounded in the middle and a neutral is landed at that point. This would not be an open delta system as Open delta is a 3 wire system with B phase grounded.
    Agree that this question should read 4-wire Delta system rather than open delta. As for the orange marking, 2015 edition states "orange in color or by other effective means."

    Not sure what the other options are but "other effective means" implies that markings other than orange are still acceptable. Pic related.

    Click image for larger version. 

Name:	nec-110-15-high-leg-marking-excerpt.jpg 
Views:	6 
Size:	142.5 KB 
ID:	378

  6. #4
  7. Join Date
    Dec 2017
    Posts
    32
    Reputation
    Quote Originally Posted by SecondGen View Post
    Agree that this question should read 4-wire Delta system rather than open delta. As for the orange marking, 2015 edition states "orange in color or by other effective means."

    Not sure what the other options are but "other effective means" implies that markings other than orange are still acceptable. Pic related.

    Click image for larger version. 

Name:	nec-110-15-high-leg-marking-excerpt.jpg 
Views:	6 
Size:	142.5 KB 
ID:	378
    In an open delta with single-phase loads, the high leg must be identified by:


    tagging or numbering

    using orange tape

    using violet tape

    any of the above


    Are we agreeing that the question is wrong ? it should be 3-Phase /4wire and Orange is the marking?

  8. #5
  9. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by akumaleon View Post
    In an open delta with single-phase loads, the high leg must be identified by:


    tagging or numbering

    using orange tape

    using violet tape

    any of the above


    Are we agreeing that the question is wrong ? it should be 3-Phase /4wire and Orange is the marking?
    Per NEC 110.15 (2017) it should be 4-wire delta, marking can be orange or "other effective means." Seems like tagging, numbering, or using any other color not prohibited by NEC (such as green) would be allowed.

  10. #6
  11. T-LOCC's Avatar
    T-LOCC is offline Junior Member Pro Subscriber
    Join Date
    Dec 2020
    Posts
    1
    Reputation
    Quote Originally Posted by Spanky123 View Post
    In an open delta with single-phase loads, the high leg must be identified by:
    Your Answer: using orange tape
    Help: NEC Section 110.15

    This was marked incorrect, but I do not understand how this is wrong after reviewing the NEC Section 110.15 It tells you to mark the high leg as orange.
    I did the same, its just a play with words to distract us.

Subscribe

Share this thread

Related Topics

  1. Open Delta Calculation
    By Kalbi_Rob in forum NETA Level 3 Exam
    Replies: 1
    Last Post: August 29, 2018, 01:32 PM
  2. Ultrasonic testing of MV switchgear <20dB requirement?
    By irishguy2010 in forum Electrical Testing Talk
    Replies: 2
    Last Post: August 16, 2018, 12:56 PM
  3. NICET Forum Now Open
    By testguy in forum News and Announcements
    Replies: 0
    Last Post: July 6, 2018, 01:10 PM
  4. Replies: 2
    Last Post: June 12, 2017, 05:06 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net