    Transformer neutral connection

    What will happen if one LT phase winding having finishing point as neutral connected to the other two phases having starting point as neutrals?

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by sahoojoge View Post
    What will happen if one LT phase winding having finishing point as neutral connected to the other two phases having starting point as neutrals?
    I'm not sure what you are asking?
    Sounds like you have a three phase transformer with wye secondary which then has two phases shorted to neutral. Next question would be is neutral grounded? Either way sounds like you have two phases shorted to neutral removing the impedance and potentially causing an arc flash waiting to happen.

    Otherwise you just described a Wye connection on a transformer, where 'A' phase wire lands and across a winding has neutral landed at the same point two windings are connected and at the other end is 'B' and 'C' phase.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    I'm not sure what you are asking?
    Sounds like you have a three phase transformer with wye secondary which then has two phases shorted to neutral. Next question would be is neutral grounded? Either way sounds like you have two phases shorted to neutral removing the impedance and potentially causing an arc flash waiting to happen.

    Otherwise you just described a Wye connection on a transformer, where 'A' phase wire lands and across a winding has neutral landed at the same point two windings are connected and at the other end is 'B' and 'C' phase.

    When I read that question the first thing that comes to mind is a three phase bank with one transformer reversed polarity. We need more clarification from OP.

  6. #4
  7. goinghot617's Avatar
    goinghot617 is offline Junior Member Pro Subscriber
    Join Date
    Sep 2017
    Posts
    4
    Reputation

    lt

    Quote Originally Posted by sahoojoge View Post
    What will happen if one LT phase winding having finishing point as neutral connected to the other two phases having starting point as neutrals?
    I believe you are basically shorting the transformer out. I have never heard of wiring a transformer this way

  8. #5
  9. Join Date
    Jul 2019
    Location
    Perth, Western Australia
    Posts
    2
    Reputation
    Quote Originally Posted by sahoojoge View Post
    What will happen if one LT phase winding having finishing point as neutral connected to the other two phases having starting point as neutrals?
    If I am not mistaken, you are trying to ask:
    What will happen if the polarity of two of the coils inside a 3 phase Y connected transformer were reversed?...

    First of all, it would be pretty hard to mix up the intended starts and finishes of each winding given the connection is most commonly by a bus bar at either the top or bottom of the coils...

    Simply put, it would likely cause voltage issues & circulating currents to flow (Seen as a higher No Load Loss result), assuming all windings share the same core. While a transformer is an AC device, the Induced Flux in the core changes with the direction of the current flow (Left hand rule). The transformer flux linkage of one coil that has been connected in the opposite direction and will be subtractive.

    In addition, if the transformer is subjected to fault currents it can cause mechanical issues (Depending on the topology of the other winding(s) on that core leg). Simply put, by design a transformers inner and outer coils should be magnetically aligned to reduce or ideally mitigate Axial forces (typically resulting in axial displacement of the windings or 'telescoping') This is because the inner and outer windings on any given core leg are most commonly wound in opposite directions so that under normal conditions, the net magnetic flux results only in a radial force (Inner winding typically compressive, outer usually expansive).

    Hope that helps.

Subscribe

Share this thread

Related Topics

  1. How to Size Transformer Neutral Resistor
    By AlexT90 in forum NETA Level 3 Exam
    Replies: 6
    Last Post: September 13, 2020, 07:18 PM
  2. Proper connection for overcurrent relay with parallel CT's
    By marvinray in forum NETA Level 4 Exam
    Replies: 12
    Last Post: October 21, 2017, 08:07 AM
  3. Neutral CT testing with ground bond
    By bwillsey88 in forum Electrical Testing Talk
    Replies: 2
    Last Post: May 18, 2017, 10:32 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net