Ground fault NEC 230.95

 Jump to latest post
    #1
  1. rynomite is offline Junior Member Pro Subscriber
    Join Date
    Jun 2016
    Posts
    1
    Reputation

    Ground fault NEC 230.95

    Click image for larger version. 

Name:	NETA sucks.PNG 
Views:	63 
Size:	10.6 KB 
ID:	382

    The exam has the correct answer as being false but I'm relatively certain ground fault protection is required here. I know there are exceptions to the rule, but I don't think this would meet any of them. Can anybody point out what I am missing? Thanks.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by rynomite View Post
    Click image for larger version. 

Name:	NETA sucks.PNG 
Views:	63 
Size:	10.6 KB 
ID:	382

    The exam has the correct answer as being false but I'm relatively certain ground fault protection is required here. I know there are exceptions to the rule, but I don't think this would meet any of them. Can anybody point out what I am missing? Thanks.
    There are a few exceptions:
    http://www.cooperindustries.com/cont...ements_GFP.pdf

    Specifically:
    "Where Ground Fault Relays are NOT Required
    There are many services and feeders where 230.95, 215.10, and 240.13 do
    not require ground fault protection including:
    1. Continuous industrial process where a non-orderly shut down would increase
    hazards.
    7. Service with six disconnects or less (230.71) where each disconnect is less than
    1000 amps. A 4000A service could be split into 5 - 800A switches.
    9. Fire Pumps
    10. For feeders where Ground Fault Protection is provided on the service (except for
    Health Care Facilities. See 517.17.)"

  4. #3
  5. phasor's Avatar
    phasor is offline Junior Member Pro Subscriber
    Join Date
    Dec 2018
    Posts
    13
    Reputation
    Quote Originally Posted by rynomite View Post
    Click image for larger version. 

Name:	NETA sucks.PNG 
Views:	63 
Size:	10.6 KB 
ID:	382

    The exam has the correct answer as being false but I'm relatively certain ground fault protection is required here. I know there are exceptions to the rule, but I don't think this would meet any of them. Can anybody point out what I am missing? Thanks.
    It's only applicable to the service, not all breakers. Article 230 is services.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by rynomite View Post
    I know there are exceptions to the rule
    Question states "all," there is your answer.

Subscribe

Share this thread

Related Topics

  1. Ground fault trips at half of setting
    By joenavymctest in forum P&C / Relay Testing Talk
    Replies: 6
    Last Post: March 6, 2020, 08:45 AM
  2. Ground Fault Exemptions
    By Kalbi_Rob in forum Electrical Testing Talk
    Replies: 2
    Last Post: June 21, 2019, 07:16 PM
  3. What is ground fault blocking capability?
    By madsenate in forum NETA Level 3 Exam
    Replies: 2
    Last Post: June 23, 2015, 11:03 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net