Hi guys,
I need to perform VLF test on one set cable. The cable rating is 12/20 kV but opeation voltage is 15 kV. So what is the right VLF Test ratings for these cables?
Thanks.
Hi guys,
I need to perform VLF test on one set cable. The cable rating is 12/20 kV but opeation voltage is 15 kV. So what is the right VLF Test ratings for these cables?
Thanks.
One thing I forgot to mention is to be aware of the termination and connected equipment as you should not exceed those ratings also.
As for voltages to test at, they are all in the table.
VLF is performed at the cable rating(or limiting component), and tan delta is based on operating voltage to ground.