Standard low-voltage circuit breakers

 Jump to latest post
    #1
  1. tavuvi is offline Junior Member
    Join Date
    Sep 2019
    Posts
    1
    Reputation

    Standard low-voltage circuit breakers

    Hello everyone.
    Currently, I am testing ACB including items of insulation resistance and contact resistance.
    I don't know the standard for low voltage circuit breaker.
    Help me please. thank you

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by tavuvi View Post
    Hello everyone.
    Currently, I am testing ACB including items of insulation resistance and contact resistance.
    I don't know the standard for low voltage circuit breaker.
    Help me please. thank you
    NEMA AB4 GUIDELINES FOR INSPECTION AND PREVENTIVE MAINTENANCE OF MOLDED CASE CIRCUIT BREAKERS USED IN COMMERCIAL AND INDUSTRIAL APPLICATIONS

    is the standard for testing LV Circuit Breakers using Primary Injection. Just be wary of voltage drop as it can only be done with a specific DC voltage, so DLRO is the preferred method. There were a few articles in NETA World discussing why voltage drop is highly unreliable.

  4. #3
  5. Join Date
    Sep 2017
    Location
    California
    Posts
    21
    Reputation
    NETA Maintenance Testing Standards (2019 Edition) give the insulation resistance values in Table 100.1
    For equipment rated at:
    250V: Test At 500 VDC and minimum resistance value is 25 megaohms.
    600V: Test at 1000 VDC and minimum resistance value is 100 megaohms.

    This is in absence of manufacturer data, and there are tables to compensate for humidity and temperature.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by tavuvi View Post
    Hello everyone.
    Currently, I am testing ACB including items of insulation resistance and contact resistance.
    I don't know the standard for low voltage circuit breaker.
    Help me please. thank you
    We usually do a 10A DLRO for contact-resistance, tolerance is +/-50% between phases. I've heard that some manufacturers will only recognize 100A test for warranty purposes.

Subscribe

Share this thread

Related Topics

  1. Replies: 11
    Last Post: March 31, 2016, 02:26 PM
  2. Looking for high current testing standard for breakers
    By Larry5443 in forum Technical Documents
    Replies: 14
    Last Post: July 21, 2015, 10:52 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net