How do you Defeat Ground Fault with Primary Injection on Eaton 310+? Trip Unit

 Jump to latest post
Page 2 of 2 FirstFirst 12
    #11
  1. Kimbo Slice is offline Member Pro Subscriber
    Join Date
    Mar 2015
    Posts
    35
    Reputation
    Quote Originally Posted by Warrengarber View Post
    How did it go?
    Nothing worked for me with this secondary test set. Had to go "in and out" to defeat the ground fault on the trip units. Thankfully I dont see these breakers that often. There was a few Eaton reps on the job as well and they didnt even have an answer for me. Not a fan of these breakers

  2. #12
  3. Join Date
    Jul 2020
    Posts
    3
    Reputation

    How should I remove the dummy connector??

    Hello!
    I just got a secondary injection test kit for a digitrip 310+ and I just can't take out this dummy connector to make it a male one... it seems to be impossible.. it is like a one-piece plastic connector...
    Any of you have done it before?
    Thank you in advance


    Quote Originally Posted by Warrengarber View Post
    It says on page 7 of the Instruction Leaflet IL5721B13H07 for the secondary test kit that you must first turn off the ground fault function before secondary testing so I would assume that there is a ground fault defeat switch. That is the test set that has a different card for each trip unit with a dial and a push button. If I remember correctly there is a module that you plug in line that has a button that defeats ground fault. Below is from page 7. Hope this helps.

    "Digitrip 310+
    Digitrip 310+ Circuit Breakers Test Procedure
    Setup
    Before testing, write down all settings in use so that they may be
    restored after tests are completed.
    To begin testing;
    1. Connect the Digitrip 310+ cable assembly (style 5721B14) into
    the side connector of the handheld unit. Plug the other end of
    the cable into the test port.
    Note: The test plug may be covered by a “dummy connector” used to
    protect the test plug pins during shipment. Ease the dummy connector
    off using a screw driver to expose the male test pins underneath.
    2. Position Trip/No Trip switch on cable assembly to the Trip position
    and set the Ground Fault switch to the “Off” position."

  4. #13
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by cmferrer View Post
    Hello!
    I just got a secondary injection test kit for a digitrip 310+ and I just can't take out this dummy connector to make it a male one... it seems to be impossible.. it is like a one-piece plastic connector...
    Any of you have done it before?
    Thank you in advance
    I usually just take a pair of needle nose pliers and pull the black cover (dummy connector) straight out with no issues. If your having issues, you might have a bent pin inside.

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. Primary Current Injection instantenous Pickup
    By changeabilities in forum Electrical Testing Talk
    Replies: 15
    Last Post: February 26, 2021, 11:50 AM
  2. Easy method for ground fault testing EATON 310 and 310+ trip units
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: October 31, 2018, 04:52 PM
  3. Primary Current Injection Test
    By changeabilities in forum Electrical Testing Talk
    Replies: 4
    Last Post: August 12, 2018, 08:17 AM
  4. Primary current injection 138kV breaker with bushing CT's
    By david2458 in forum Electrical Testing Talk
    Replies: 1
    Last Post: April 12, 2018, 05:27 AM
  5. Replies: 1
    Last Post: March 2, 2016, 04:59 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net