There are exemptions to 230.95:
http://www.cooperindustries.com/cont...ements_GFP.pdf
Where Ground Fault Relays are NOT Required
There are many services and feeders where 230.95, 215.10, and 240.13 do
not require ground fault protection including:
1. Continuous industrial process where a non-orderly shut down would increase
hazards.
2. All services or feeders where the disconnect is less than 1000 amps.
3. All 208Y/120 Volt, 3ø, 4W (wye) services or feeders.
4. All single-phase services or feeders including 240/120 Volt.
5. High or medium voltage services or feeders. (See NEC® 240.13 and 215.10 for
feeder requirements.)
6. All services or feeders on delta systems (grounded or ungrounded) such as 240
Volt, 3ø, 3W delta, or 240 Volt, 3ø, 4W delta with midpoint tap.
7. Service with six disconnects or less (230.71) where each disconnect is less than
1000 amps. A 4000A service could be split into 5 - 800A switches.
8. Resistance or impedance grounded systems.
9. Fire Pumps
10. For feeders where Ground Fault Protection is provided on the service (except for
Health Care Facilities. See 517.17.)