4. Ground fault protection is required by the NEC for all solidly grounded 480Y/277V system breakers rated 1000A or greater.
Your Answer: True
Correct Answer: False
Am I reading 230-95 wrong? - "Ground-fault protection of equipment shall be provided for solidly grounded wye electrical services of more than 150 volts to ground but not exceeding 600 volts phase-to-phase for each service disconnect rated 1000 amperes or more.
Seems it should be true?