    Tan Delta versus Partial Discharge testing on cables

    Thoughts on this? What is the preferred test for all of you, and why?






    www.taifaengineering.com

  2. #2
  3. Join Date
    Jun 2017
    Posts
    25
    Reputation
    Quote Originally Posted by TaifaEngineering View Post
    Thoughts on this? What is the preferred test for all of you, and why?






    www.taifaengineering.com
    It all depends on the application. In general I feel that the Tan Delta is the better test but it is more invasive the cable must be de-energized and made safe. The Partial Discharge testing if they have the hardware installed can be done live.

    In general for a site that has infrequent shutdowns Partial Discharge would be the way to go and it can provide information on problem cables that you can then check with Tan Delta during a shutdown.

  4. #3
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Nick1234 View Post
    It all depends on the application. In general I feel that the Tan Delta is the better test but it is more invasive the cable must be de-energized and made safe. The Partial Discharge testing if they have the hardware installed can be done live.

    In general for a site that has infrequent shutdowns Partial Discharge would be the way to go and it can provide information on problem cables that you can then check with Tan Delta during a shutdown.
    My last company recommended performing Online PD annually, and every 5 years performing Tan-Delta or Offline Partial Discharge since OLPD doesn't detect minor electrical treeing, while the offline test can.

    I believe the overall difference lies in the cost and safety placed on the customer to work around. Tan-delta is cheaper (I have determined failure in a cable within 3 months with TD), but Offline Partial Discharge is much more accurate, and Online Partial Discharge is more convenient to continued operations.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by TaifaEngineering View Post
    Thoughts on this? What is the preferred test for all of you, and why?
    www.taifaengineering.com
    Offline PD is the most accurate if you are going to take the cable down but is really specialized and expensive. Tan Delta combined with VLF will give you a good baseline for comparison in the future and is much cheaper. Online PD is a good non-distructive test, but like an infrared scan its only useful for monitoring, not a replacement for offline maintenance.

    From NETA World Spring 2017: Tan delta tests the health of the insulation as an average value of the length of the cable, and therefore, small sections with significant defects cannot be detected. Partial discharge detects these small defects but cannot detect aging effects (like water trees) until they result in discharge. Thus, these two tests are complementary, and it is advisable to do both at the commissioning of any cable.

    https://www.eatechnology.com/america...17_FlowONE.pdf

  8. #5
  9. Join Date
    Jul 2021
    Posts
    3
    Reputation
    Quote Originally Posted by SecondGen View Post
    Offline PD is the most accurate if you are going to take the cable down but is really specialized and expensive. Tan Delta combined with VLF will give you a good baseline for comparison in the future and is much cheaper. Online PD is a good non-distructive test, but like an infrared scan its only useful for monitoring, not a replacement for offline maintenance.

    From NETA World Spring 2017: Tan delta tests the health of the insulation as an average value of the length of the cable, and therefore, small sections with significant defects cannot be detected. Partial discharge detects these small defects but cannot detect aging effects (like water trees) until they result in discharge. Thus, these two tests are complementary, and it is advisable to do both at the commissioning of any cable.

    https://www.eatechnology.com/america...17_FlowONE.pdf
    Thanks for the reference, I wrote that article. Online PD is the way to go to test large populations or to test frequently. If you aren't seeing during normal operating conditions, do you really care that you get PD inception at 1.5 nominal? If you permanently install RFCT/HFCT, then you can test any time in a safe, shirt sleeve environment.

    Once you start seeing PD online, then think about running offline tests. I feel that once you go to the pain of getting an outage and bringing in a test company, you might as well to Tan Delta and PD.

  10. #6
  11. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Billhig View Post
    Thanks for the reference, I wrote that article. Online PD is the way to go to test large populations or to test frequently. If you aren't seeing during normal operating conditions, do you really care that you get PD inception at 1.5 nominal? If you permanently install RFCT/HFCT, then you can test any time in a safe, shirt sleeve environment.

    Once you start seeing PD online, then think about running offline tests. I feel that once you go to the pain of getting an outage and bringing in a test company, you might as well to Tan Delta and PD.
    Great article and important points to remember, thanks for stopping by!

Subscribe

Share this thread

Related Topics

  1. Safely discharge HV feeder using load break disconnect switch (procedure)
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 3
    Last Post: August 17, 2020, 01:08 PM
  2. Minimum discharge time at end of cable test
    By Cldpmu in forum NETA Level 2 Exam
    Replies: 3
    Last Post: December 21, 2018, 10:08 PM
  3. Tan / Delta or Power Factor Testing of Dry Type Transformer
    By mask12900 in forum Electrical Testing Talk
    Replies: 1
    Last Post: January 1, 2018, 08:41 PM
  4. Partial Discharge Data Interpretation
    By ies0900012 in forum Electrical Testing Talk
    Replies: 2
    Last Post: July 21, 2016, 06:27 PM
  5. How much spacing should you have when testing cables?
    By cjones09 in forum Safety and Arc Flash Talk
    Replies: 5
    Last Post: September 21, 2015, 02:52 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net