    How do you Primary inject the neutral of a 4 pole circuit breaker?

    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I’m guessing is for over current on the return?

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by TrapFlyVenus View Post
    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I’m guessing is for over current on the return?
    Test just like any other pole, I've run into a lot of these on Square D Masterpacts in data center UPS systems.

  4. #3
  5. Join Date
    Mar 2019
    Posts
    7
    Reputation
    Quote Originally Posted by TrapFlyVenus View Post
    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I’m guessing is for over current on the return?
    Test just like the other phases. Sometimes the neutral pole doesn't have overcurrent protection so don't be surprised if you try to test it and it doesn't trip. Is it a molded case or insulated case?

  6. #4
  7. Join Date
    Jun 2017
    Posts
    25
    Reputation
    Quote Originally Posted by TrapFlyVenus View Post
    How do you guys Primary injection the neutral of a 4 pole breaker? It has a setting which I’m guessing is for over current on the return?
    The neutral pole you test like any other pole like has been said before. You have to realize that all neutral poles are different on different breakers.

    Some neutral poles have no protection and are just a switch for that pole, some have settings that will trip at half or full value of the trip settings. Others only have some trip settings, like the large Magnum DS with 8 poles, on those there are 2 neutral poles and the only trip fiction on the neutral is ground fault and maintenance mode.

Subscribe

Share this thread

Related Topics

  1. Primary Injection Minimum Breaker Size As Per NETA
    By dnigra in forum Electrical Testing Talk
    Replies: 6
    Last Post: January 27, 2021, 02:50 PM
  2. Learning how to primary current inject breakers
    By lazo2794 in forum Electrical Testing Talk
    Replies: 4
    Last Post: December 3, 2020, 07:53 PM
  3. Circuit Breaker Primary Injection Excel Sheet
    By changeabilities in forum Technical Documents
    Replies: 3
    Last Post: June 24, 2020, 09:08 AM
  4. Primary current injection 138kV breaker with bushing CT's
    By david2458 in forum Electrical Testing Talk
    Replies: 1
    Last Post: April 12, 2018, 05:27 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net