Liquid samples that were drawn when the liquid was below 32 degrees F

 Jump to latest post
    #1
  1. Join Date
    Nov 2019
    Posts
    2
    Reputation

    Liquid samples that were drawn when the liquid was below 32 degrees F

    Liquid samples that were drawn when the liquid was below 32 degrees F

    What happens when this is done?

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by CameronMHayes View Post
    Liquid samples that were drawn when the liquid was below 32 degrees F

    What happens when this is done?
    Is there somewhere you read 32F? Only thing I have read is the following:

    WARNING:
    Three-phase pad-mounted transformers use
    conventional transformer oil, R-Temp fluid, or
    Envirotemp™ FR3™ fluid for an insulating liquid.When
    the insulating liquid temperature is less than -20°C
    (-4°F) for conventional transformer oil, less than 0°C
    (32°F) for R-Temp fluid or less than -10°C (14°F) for
    Envirotemp™ FR3™ fluid, viscosity is reduced, which
    may reduce make and break capabilities of loadbreak
    devices. Below these temperatures, under-oil loadbreak
    accessories should not be used to make or break a
    load. Instead, de-energize transformer from a remote
    upstream source before operating under-oil loadbreak
    devices.

  4. #3
  5. Join Date
    Nov 2019
    Posts
    2
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Is there somewhere you read 32F? Only thing I have read is the following:

    WARNING:
    Three-phase pad-mounted transformers use
    conventional transformer oil, R-Temp fluid, or
    Envirotemp™ FR3™ fluid for an insulating liquid.When
    the insulating liquid temperature is less than -20°C
    (-4°F) for conventional transformer oil, less than 0°C
    (32°F) for R-Temp fluid or less than -10°C (14°F) for
    Envirotemp™ FR3™ fluid, viscosity is reduced, which
    may reduce make and break capabilities of loadbreak
    devices. Below these temperatures, under-oil loadbreak
    accessories should not be used to make or break a
    load. Instead, de-energize transformer from a remote
    upstream source before operating under-oil loadbreak
    devices.

    I was doing the Neta I test Prep and that was one of the questions that was given to me and the only one I missed. When I missed it unlike other times it only gave me the option to discuss it instead of get information.

    Thank you so very much for answering the question for me it is much appreciated!!!

  6. #4
  7. Join Date
    Jan 2020
    Posts
    26
    Reputation
    Above or below freezing point shouldn't have any effect on an oil sample (other than it taking longer to extract).

    Operation of equipment itself would be a different topic.

Subscribe

Share this thread

Related Topics

  1. Testing liquid filled transformers with load break bushings
    By GDerr81 in forum Electrical Testing Talk
    Replies: 2
    Last Post: November 15, 2016, 02:47 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net