Originally Posted by
Kalbi_Rob
I only tell techs to not test fuses on PT's because you are using a 10A ductor and most PT fuses are 1A or less. Always verify the fuse size before testing, or you might be buying new fuses.
As for any other piece of equipment, you can verify the fuse is still good and if they are experiencing damage.
I had a customer that was running single phase on a MV contactor starter due to a blown fuse, but when we went to replace it, the engineer told me it wasn't possible to be single phase on the motor cause he would know about it. Went out the the operator and found out they had replaced 2 sets of bearings (over 2 year period), and were currently replacing the motor due to overheating conditions but never realized it was just a blown fuse.