Can this CT produce enough voltage to trip a relay?

 Jump to latest post
Page 2 of 2 FirstFirst 12
    #11
  1. Dublin is offline Junior Member
    Join Date
    Jan 2017
    Posts
    1
    Reputation
    Quote Originally Posted by zslater View Post
    You do have to consider the C20. That is the maximum voltage that the CT is able to produce. The circuit requires 25V in order to operate. Thus this CT will not work as a relaying CT. However, it will work as a metering CT because the total circuit burden is .25 which is less than the .9 burden rating the CT has.

    I attached a link to a great powerpoint that has this exact question in it.

    https://nanopdf.com/queue/instrument...E1MC4yNDAuMjE3

    Hope this helps
    How do you know that it requires 25V in order to operate the circuit?

    This would most likely be able to operate the relay. Most protection is set far below the 20xIn rule of thumb if the question was "Is this CT correctly sized to be used as a protection CT?" I would agree that it is not, but the question was would this operate the protection, and there is not enough information to answer that,

    In all likelihood, it would operate the protection unless the protection is exclusively very high current trips such as an instantaneous trip.

    To know if this would operate the relay, we would need to know the protection setpoints of the relay.

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. What would cause a generator to trip on 32R?
    By djohnson18 in forum NETA Level 3 Exam
    Replies: 4
    Last Post: January 10, 2019, 11:28 AM
  2. Overpotential test voltage for low-voltage switchgear
    By AlexT90 in forum Electrical Testing Talk
    Replies: 6
    Last Post: March 18, 2018, 08:29 PM
  3. Replies: 1
    Last Post: March 2, 2016, 04:59 PM
  4. Trip contact operation after relay testing
    By DetroitLions in forum NETA Level 3 Exam
    Replies: 0
    Last Post: January 30, 2016, 09:16 PM
  5. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 11:14 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net