I think yes. 100ft x .0025ohm/ft = 0.25ohm < .9ohm so its ok.
I think yes. 100ft x .0025ohm/ft = 0.25ohm < .9ohm so its ok.
11. A given CT is rated 600:5, C20, 0.3 B 0.9. Can this CT produce enough voltage to trip a relay (with near-zero burden) 50 feet away if connected to the relay with #14 awg (.0025 ohms/ ft) wire?
Not sure how to calculate this, can someone please help?
well I give you what the "circuit" values are. (the Z and voltage drop of your wire)
usually you will have the relay Z or VA to add to your wire... but in this case your relay burden is neglected.
A 0.3 B 0.9 rated metering-class CT means it will operate within 0.3 percent accuracy if the secondary burden does not exceed 0.9 ohms.
Thank you. No need to consider the "C20" or "B" (CT Class)?
Also, the question was "will it produce enough voltage to trip the relay?
- If this is protection class, then the 0.9 means Volts @ 20x CT rating, NOT not to exceed 0.9 ohms
- How do we know how much voltage is required to trip the relay?
Cheers!
-if this is a relaying CT (protection) ? saying C20 ... means '20' Maximum in Volts @ 20 times CT Amp Rating.
and with a CT ratio of 600:'5'. in that case it's V=I*R where if you need Ohms BURDEN you do R=V/I . Just like you said with 20x CT rating;
20V/ (5A*20) = 0.2 Ohms
for a C100 runing 5A with 20X --> it will be 1 Ohms
C200 --> 2 ohms
C400 --> 4 ohms
C50 --> 0.5 ohms
-To me it looks like your question (trick question) its a Metering CT and its based on how to calculate the total burden of your circuit.
I would have done the following;
0.0025 ohms/ft x 50 ft = 0.125 ohms one way of my wire so 2x = 0.25 ohms
neglect the relays Z etc...
The secondary voltage is my total resistance X CT rated amps = 0.25*5= 1.25 Volts
(on the first post I forgot to double the wire of the circuit sense you need 2 wires for close circuit)
Last edited by akumaleon; January 24, 2020 at 01:04 PM.
You do have to consider the C20. That is the maximum voltage that the CT is able to produce. The circuit requires 25V in order to operate. Thus this CT will not work as a relaying CT. However, it will work as a metering CT because the total circuit burden is .25 which is less than the .9 burden rating the CT has.
I attached a link to a great powerpoint that has this exact question in it.
https://nanopdf.com/queue/instrument...E1MC4yNDAuMjE3
Hope this helps