    Can this CT produce enough voltage to trip a relay?

    I think yes. 100ft x .0025ohm/ft = 0.25ohm < .9ohm so its ok.

  2. #2
  3. mmacdonell is offline Junior Member Pro Subscriber
    Join Date
    May 2019
    Posts
    17
    Reputation

    11. A given CT is rated 600:5, C20, 0.3 B 0.9. Can this CT produce enough voltage to

    11. A given CT is rated 600:5, C20, 0.3 B 0.9. Can this CT produce enough voltage to trip a relay (with near-zero burden) 50 feet away if connected to the relay with #14 awg (.0025 ohms/ ft) wire?

    Not sure how to calculate this, can someone please help?

  4. #3
  5. Join Date
    Dec 2017
    Posts
    32
    Reputation
    Quote Originally Posted by mmacdonell View Post
    11. A given CT is rated 600:5, C20, 0.3 B 0.9. Can this CT produce enough voltage to trip a relay (with near-zero burden) 50 feet away if connected to the relay with #14 awg (.0025 ohms/ ft) wire?

    Not sure how to calculate this, can someone please help?

    So you have 0.0025 ohms/ft x 50 ft = 0.125 ohms of your total wire circuit.

    5A from your CT (600:5) so you can produce: V=I*R= 5*0.125 = 0.625V

    I believe that is the voltage you are looking for.

    And your total burden in VA would just be 0.625V*5A= 3.125VA

  6. #4
  7. mmacdonell is offline Junior Member Pro Subscriber
    Join Date
    May 2019
    Posts
    17
    Reputation
    Quote Originally Posted by akumaleon View Post
    So you have 0.0025 ohms/ft x 50 ft = 0.125 ohms of your total wire circuit.

    5A from your CT (600:5) so you can produce: V=I*R= 5*0.125 = 0.625V

    I believe that is the voltage you are looking for.

    And your total burden in VA would just be 0.625V*5A= 3.125VA
    So no need to consider the accuracy, accuracy class or max burden?

  8. #5
  9. Join Date
    Dec 2017
    Posts
    32
    Reputation
    Quote Originally Posted by mmacdonell View Post
    So no need to consider the accuracy, accuracy class or max burden?
    well I give you what the "circuit" values are. (the Z and voltage drop of your wire)
    usually you will have the relay Z or VA to add to your wire... but in this case your relay burden is neglected.


    A 0.3 B 0.9 rated metering-class CT means it will operate within 0.3 percent accuracy if the secondary burden does not exceed 0.9 ohms.

  10. #6
  11. mmacdonell is offline Junior Member Pro Subscriber
    Join Date
    May 2019
    Posts
    17
    Reputation
    Quote Originally Posted by akumaleon View Post
    well I give you what the "circuit" values are. (the Z and voltage drop of your wire)
    usually you will have the relay Z or VA to add to your wire... but in this case your relay burden is neglected.


    A 0.3 B 0.9 rated metering-class CT means it will operate within 0.3 percent accuracy if the secondary burden does not exceed 0.9 ohms.
    Thank you. No need to consider the "C20" or "B" (CT Class)?

    Also, the question was "will it produce enough voltage to trip the relay?
    - If this is protection class, then the 0.9 means Volts @ 20x CT rating, NOT not to exceed 0.9 ohms
    - How do we know how much voltage is required to trip the relay?

    Cheers!

  12. #7
  13. Join Date
    Dec 2017
    Posts
    32
    Reputation
    Quote Originally Posted by mmacdonell View Post
    Thank you. No need to consider the "C20" or "B" (CT Class)?

    Also, the question was "will it produce enough voltage to trip the relay?
    - If this is protection class, then the 0.9 means Volts @ 20x CT rating, NOT not to exceed 0.9 ohms
    - How do we know how much voltage is required to trip the relay?

    Cheers!

    -if this is a relaying CT (protection) ? saying C20 ... means '20' Maximum in Volts @ 20 times CT Amp Rating.

    and with a CT ratio of 600:'5'. in that case it's V=I*R where if you need Ohms BURDEN you do R=V/I . Just like you said with 20x CT rating;
    20V/ (5A*20) = 0.2 Ohms

    for a C100 runing 5A with 20X --> it will be 1 Ohms
    C200 --> 2 ohms
    C400 --> 4 ohms
    C50 --> 0.5 ohms

    -To me it looks like your question (trick question) its a Metering CT and its based on how to calculate the total burden of your circuit.
    I would have done the following;

    0.0025 ohms/ft x 50 ft = 0.125 ohms one way of my wire so 2x = 0.25 ohms
    neglect the relays Z etc...
    The secondary voltage is my total resistance X CT rated amps = 0.25*5= 1.25 Volts
    (on the first post I forgot to double the wire of the circuit sense you need 2 wires for close circuit)
    Last edited by akumaleon; January 24, 2020 at 01:04 PM.

  14. #8
  15. mmacdonell is offline Junior Member Pro Subscriber
    Join Date
    May 2019
    Posts
    17
    Reputation
    Quote Originally Posted by akumaleon View Post
    -if this is a relaying CT (protection) ? saying C20 ... means '20' Maximum in Volts @ 20 times CT Amp Rating.

    and with a CT ratio of 600:'5'. in that case it's V=I*R where if you need Ohms BURDEN you do R=V/I . Just like you said with 20x CT rating;
    20V/ (5A*20) = 0.2 Ohms

    for a C100 runing 5A with 20X --> it will be 1 Ohms
    C200 --> 2 ohms
    C400 --> 4 ohms
    C50 --> 0.5 ohms

    -To me it looks like your question (trick question) its a Metering CT and its based on how to calculate the total burden of your circuit.
    I would have done the following;

    0.0025 ohms/ft x 50 ft = 0.125 ohms one way of my wire so 2x = 0.25 ohms
    neglect the relays Z etc...
    The secondary voltage is my total resistance X CT rated amps = 0.25*5= 1.25 Volts
    (on the first post I forgot to double the wire of the circuit sense you need 2 wires for close circuit)
    Thanks, I agree with you there but then ultimately the questions is do you have enough voltage to trip the relay. So how would we know the required voltage?

  16. #9
  17. Join Date
    Dec 2017
    Posts
    32
    Reputation
    Quote Originally Posted by mmacdonell View Post
    Thanks, I agree with you there but then ultimately the questions is do you have enough voltage to trip the relay. So how would we know the required voltage?
    V= I * (Rs + Rb)

  18. #10
  19. Join Date
    Jan 2018
    Posts
    7
    Reputation
    Quote Originally Posted by mmacdonell View Post
    Thank you. No need to consider the "C20" or "B" (CT Class)?

    Also, the question was "will it produce enough voltage to trip the relay?
    - If this is protection class, then the 0.9 means Volts @ 20x CT rating, NOT not to exceed 0.9 ohms
    - How do we know how much voltage is required to trip the relay?

    Cheers!
    You do have to consider the C20. That is the maximum voltage that the CT is able to produce. The circuit requires 25V in order to operate. Thus this CT will not work as a relaying CT. However, it will work as a metering CT because the total circuit burden is .25 which is less than the .9 burden rating the CT has.

    I attached a link to a great powerpoint that has this exact question in it.

    https://nanopdf.com/queue/instrument...E1MC4yNDAuMjE3

    Hope this helps

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. What would cause a generator to trip on 32R?
    By djohnson18 in forum NETA Level 3 Exam
    Replies: 4
    Last Post: January 10, 2019, 11:28 AM
  2. Overpotential test voltage for low-voltage switchgear
    By AlexT90 in forum Electrical Testing Talk
    Replies: 6
    Last Post: March 18, 2018, 08:29 PM
  3. Replies: 1
    Last Post: March 2, 2016, 04:59 PM
  4. Trip contact operation after relay testing
    By DetroitLions in forum NETA Level 3 Exam
    Replies: 0
    Last Post: January 30, 2016, 09:16 PM
  5. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 11:14 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net