Ground Fault Protection

    #1
  1. Trevorvaligura is offline Junior Member Pro Subscriber
    Join Date
    May 2015
    Posts
    7
    Reputation

    Ground Fault Protection

    What overcurrent relay could you install between phase and ground? This needs to be changed, the relay (CT) would be installed on the neutral conductor or around all phases (residual) but not between phase and ground.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Trevorvaligura View Post
    What overcurrent relay could you install between phase and ground? This needs to be changed, the relay (CT) would be installed on the neutral conductor or around all phases (residual) but not between phase and ground.
    Might be trivial, but residual ground fault is the addition of a Neutral ct to the existing breaker ct's, while zero sequence ground fault is the addition of a CT that encompasses all phases including the neutral.