Transformer Primary Injection Testing Calculation

 Jump to latest post
Page 1 of 2 12 LastLast
    #1
  1. Join Date
    May 2017
    Posts
    7
    Reputation

    Transformer Primary Injection Testing Calculation

    Quote Originally Posted by slts1991 View Post
    Thanks for the input. Here are some answers

    Original Question: A primary injection is to be performed on a transformer 138kV/25kV, 2500kva, 8%Z using a 480V generator connected to the high side with the low side grounded. The expected current in the high side is?


    7. You did not specify the xfmr connection but assuming it is Delta/Wye my calculation is 3007.12 A primary
    Didn't read all the answers but this one jumped out and just slapped me as very high. I think that if no three phase connection is given one assumes a single phase transformer. If I tell you I am standing here with a 480V to 120V transformer in my hand you would assume one transformer with a turns ratio of 4 to 1 and a primary voltage of 480 volts.

    Ok - so the full load current at 138,000V and 2,500,000 VA is 18.116 A. At 8%Z with a shorted secondary you would multiply that by 12.5 so at rated voltage you have 226.45 amps Isc. But you are only applying 480V so you would get, proportionately, 0.787 AMPS. Generally, if I specify that a transformer is (for example) 10%Z that means that with the secondary shorted it will take 10% of the rated primary voltage to get full load current. www.cttestset.com

  2. #2
  3. Join Date
    Sep 2017
    Posts
    3
    Reputation
    Quote Originally Posted by Vernon View Post
    Ok - so the full load current at 138,000V and 2,500,000 VA is 18.116 A. At 8%Z with a shorted secondary you would multiply that by 12.5 so at rated voltage you have 226.45 amps Isc. But you are only applying 480V so you would get, proportionately, 0.787 AMPS. Generally, if I specify that a transformer is (for example) 10%Z that means that with the secondary shorted it will take 10% of the rated primary voltage to get full load current. www.cttestset.com
    Hi Vernon, can you explain why we multiply by 12.5 and why we don't use three phase voltage in the calculation? Thank you.

  4. #3
  5. Join Date
    May 2018
    Posts
    25
    Reputation
    Quote Originally Posted by Vernon View Post
    Didn't read all the answers but this one jumped out and just slapped me as very high. I think that if no three phase connection is given one assumes a single phase transformer. If I tell you I am standing here with a 480V to 120V transformer in my hand you would assume one transformer with a turns ratio of 4 to 1 and a primary voltage of 480 volts.

    Ok - so the full load current at 138,000V and 2,500,000 VA is 18.116 A. At 8%Z with a shorted secondary you would multiply that by 12.5 so at rated voltage you have 226.45 amps Isc. But you are only applying 480V so you would get, proportionately, 0.787 AMPS. Generally, if I specify that a transformer is (for example) 10%Z that means that with the secondary shorted it will take 10% of the rated primary voltage to get full load current. www.cttestset.com
    I can follow all the math except where the 12.5 number came from. Can anyone fill me in on what I missed?

  6. #4
  7. Join Date
    May 2018
    Posts
    25
    Reputation
    Quote Originally Posted by Vernon View Post
    Didn't read all the answers but this one jumped out and just slapped me as very high. I think that if no three phase connection is given one assumes a single phase transformer. If I tell you I am standing here with a 480V to 120V transformer in my hand you would assume one transformer with a turns ratio of 4 to 1 and a primary voltage of 480 volts.

    Ok - so the full load current at 138,000V and 2,500,000 VA is 18.116 A. At 8%Z with a shorted secondary you would multiply that by 12.5 so at rated voltage you have 226.45 amps Isc. But you are only applying 480V so you would get, proportionately, 0.787 AMPS. Generally, if I specify that a transformer is (for example) 10%Z that means that with the secondary shorted it will take 10% of the rated primary voltage to get full load current. www.cttestset.com
    I see it now...

    (kVA x 100)/(kV x %Z)


    Therefore,

    (2,500,000VA x 100)/(138,000V x 8) = 226.449A


    But at 480VAC vice 138,000VAC so,

    138,000/480 = 287.5


    So dividing the short-circuit primary amps by the voltage ratio difference:

    226.449A/287.5 = 0.787A

  8. #5
  9. Join Date
    Jan 2019
    Posts
    19
    Reputation
    Quote Originally Posted by ddd675 View Post
    7. A primary injection is to be performed on a transformer 138kV/25kV, 2500kva, 8%Z using a 480V generator connected to the high side with the low side grounded. The expected current in the high side is?
    Assuming that the answer from the practice tests is correct, I believe I have finally satisfied myself with a reasonable solution to this problem.

    - Assume the xfmr is single-phase since no other information is given.
    - Using SC calculation, we find that the secondary fault current in a SC would be 1,250A.
    - Knowing the secondary voltage and current, we can solve for the reactance in the secondary coil, giving 20 ohms @ 60Hz (another assumption).
    - Changing gears; we now have a known secondary impedance since the secondary is grounded (20 ohms).
    - With the fixed turns ratio of 5.52, we find that applying 480 to the primary gives us 86.9V on the secondary.
    - Apply Ohm's Law to find secondary current over our 20 ohm impedance (4.35A).
    - Again, use the TR of 5.52 to find what level of primary current will cause 4.35A in the secondary.

    With all these assumptions, I come up with 0.787A of primary current.

    This reference pointed me in the right direction. Until now, all the solutions I have seen on here were as clear as mud. https://www.eaton.com/ecm/groups/pub...wp009001en.pdf
    Last edited by young_dad; November 25, 2019 at 07:13 PM.

  10. #6
  11. Join Date
    Jan 2019
    Posts
    19
    Reputation
    Quote Originally Posted by roberts311 View Post
    I can follow all the math except where the 12.5 number came from. Can anyone fill me in on what I missed?
    It just popped into my head the other night: 100% ÷ 8% = 12.5. Vernon multiplies by 12.5 rather than dividing by 0.08.

  12. #7
  13. mmacdonell is offline Junior Member Pro Subscriber
    Join Date
    May 2019
    Posts
    17
    Reputation
    A primary injection is to be performed on a D-Y transformer rated 138kV/25kV, 2500kva, 8%Z using a 480V generator connected to the high side with the low side grounded. What is the expected current on the high side?

    0.262A
    0.455A
    0.787A
    1.36A

  14. #8
  15. Join Date
    Sep 2019
    Posts
    3
    Reputation

    acs69

    Quote Originally Posted by mmacdonell View Post
    A primary injection is to be performed on a D-Y transformer rated 138kV/25kV, 2500kva, 8%Z using a 480V generator connected to the high side with the low side grounded. What is the expected current on the high side?

    0.262A
    0.455A
    0.787A
    1.36A
    Answer: 0.455A

  16. #9
  17. carl21 is offline Junior Member Pro Subscriber
    Join Date
    Feb 2021
    Posts
    5
    Reputation

    what is the point of primary injection of a transformer?

    i understand the math, but have never seen or heard of this done. hopefully this is just an old method to something we currently do in its place for testing.

  18. #10
  19. jrm5116 is offline Junior Member
    Join Date
    Aug 2021
    Posts
    10
    Reputation
    I got 1.364A on the high side.

    So using a power base of 2500kVA and a voltage base of 138kv, the actual impedance seen by the high side would be

    (.08)*(138kV^2)/(2500kVA) = 609.41 Ohms seen by the high side.
    percent imp*(Base Voltage Squared)/(Base KVA Squared)

    the equivalent circuit would be a 480V source to a three 609.41 impedances connected in a Delta.

    the single phase equivalent using ohms law would be 480V = (Line Current/Square Root of 3)* 609.41 Ohm

    Or

    I = 480/609.41*1.732 = 1.364A

    If I use a Y connection. I would get the .45476A.
    If I solve for phase current instead of line current, I'd get .7876A

    Did anyone else get this answer?

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. Primary Current Injection instantenous Pickup
    By changeabilities in forum Electrical Testing Talk
    Replies: 15
    Last Post: February 26, 2021, 11:50 AM
  2. long time delay primary injection testing
    By KLLU26 in forum Electrical Testing Talk
    Replies: 3
    Last Post: April 4, 2019, 10:52 AM
  3. Primary Current Injection Test
    By changeabilities in forum Electrical Testing Talk
    Replies: 4
    Last Post: August 12, 2018, 08:17 AM
  4. Primary current injection 138kV breaker with bushing CT's
    By david2458 in forum Electrical Testing Talk
    Replies: 1
    Last Post: April 12, 2018, 05:27 AM