When is Ground Fault protection required on 480V system?

    #1
  1. Join Date
    Mar 2015
    Posts
    6
    Reputation

    When is Ground Fault protection required on 480V system?

    [QUOTE=slts1991;8503]

    15.B (not required, NEC 700.6(D))

    The chapter you are citing refers to emergency systems.

    I would think the appropriate chapter is:
    "230.95 Ground-Fault Protection of Equipment. Ground-fault protection of equipment shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more. The grounded conductor for the solidly grounded wye system shall be connected directly to ground through a grounding electrode system, as specified in 250.50, without inserting any resistor or impedance device. The rating of the service disconnect shall be considered to be the rating of the largest fuse that can be installed or the highest continuous current trip setting for which the actual over current device installed in a circuit breaker is rated or can be adjusted."

    Thanks

  2. #2
  3. Join Date
    Mar 2015
    Posts
    6
    Reputation

    Correction

    [QUOTE=tallyson71;8580]
    Quote Originally Posted by slts1991 View Post

    15.B (not required, NEC 700.6(D))

    The chapter you are citing refers to emergency systems.

    I would think the appropriate chapter is:
    "230.95 Ground-Fault Protection of Equipment. Ground-fault protection of equipment shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more. The grounded conductor for the solidly grounded wye system shall be connected directly to ground through a grounding electrode system, as specified in 250.50, without inserting any resistor or impedance device. The rating of the service disconnect shall be considered to be the rating of the largest fuse that can be installed or the highest continuous current trip setting for which the actual over current device installed in a circuit breaker is rated or can be adjusted."

    Thanks
    From a subsequent post it looks like this question may have referred to emergency systems, which should not trip.

  4. #3
  5. Join Date
    Jan 2015
    Posts
    48
    Reputation
    [QUOTE=tallyson71;8580]
    Quote Originally Posted by slts1991 View Post

    15.B (not required, NEC 700.6(D))

    The chapter you are citing refers to emergency systems.

    I would think the appropriate chapter is:
    "230.95 Ground-Fault Protection of Equipment. Ground-fault protection of equipment shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more. The grounded conductor for the solidly grounded wye system shall be connected directly to ground through a grounding electrode system, as specified in 250.50, without inserting any resistor or impedance device. The rating of the service disconnect shall be considered to be the rating of the largest fuse that can be installed or the highest continuous current trip setting for which the actual over current device installed in a circuit breaker is rated or can be adjusted."

    Thanks
    I think I got confused because I had both questions on my tests. Last time I went and passed the test I had the one with emergency systems. You need to read the question properly and not mistake the two of them during your test. On emergency is not required except for audio and visual.

Subscribe

Share this thread

Related Topics

  1. Ground Fault Protection
    By Trevorvaligura in forum NETA Level 3 Exam
    Replies: 1
    Last Post: February 18, 2020, 07:12 AM
  2. Ground fault protection required by NEC
    By ecubed in forum NETA Level 3 Exam
    Replies: 5
    Last Post: January 16, 2020, 05:31 PM
  3. Zone ground fault protection. Blocking and tripping?
    By marvinray in forum NETA Level 4 Exam
    Replies: 3
    Last Post: October 6, 2017, 03:42 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net