Meggerman
Hello Bob, you are not alone in experiencing the inconsistent readings for C2 across various bushings. I attended a presentation from ABB at a conference in New Brunswick Canada in 2019 - specifically on C2 testing, construction and value of the C2 test. In the presentation, David M Geibbel - Technical Director ABB Alamo TN presented evidence and statistical data showing that C2 was not a reliable indicator of health of a bushing - in other words, would one "condemn/change" a bushing based on the C2 result. David clearly indicated the answer to be NO. As well, when we asked ABB Bushing Headquarters in Sweden for a statement on C2 testing, they formally wrote back to state that C2 is not considered in failing or passing a bushing.
C2 testing is subject to many influences which are not seen in the C1 testing. Comparison to nameplate PF is contentious leaving only capacitance as a comparison. Trending, although useful in C1 testing is both difficult to keep up (as my experience, most users do not maintain the needed trending history)
In my opinion, C1 testing is your best determinent for health, and one MUST compare to nameplate PF and temperature correction is mandatory if at any extreme temperatures above 25C or below 15C.
There are new methods of testing bushings where the bushings are tested at both 60Hz PF and at lower frequency - down to 1 Hz PF with clear evidence of detecting issues very early in the degradation stages of the bushing - and one can compare the other phase results to determine if one specific bushing is changing.
Hope this is useful to you.