    How to verify MV Cable Test Reports?

    In reviewing a MV Cable Test Report is there an industry standard to compare the resulted values to verify if the values provided in the report are acceptable. For example looking at a MV test report for a Hi-Pot test of MV conductors stepped over time 1 - 6 then Final for 15min. at maximum values. Also if there is a difference between phases and ground would the standard list acceptable delta between phases that would be acceptable. thanks.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by mike01 View Post
    In reviewing a MV Cable Test Report is there an industry standard to compare the resulted values to verify if the values provided in the report are acceptable. For example looking at a MV test report for a Hi-Pot test of MV conductors stepped over time 1 - 6 then Final for 15min. at maximum values. Also if there is a difference between phases and ground would the standard list acceptable delta between phases that would be acceptable. thanks.
    First, it would be helpful to know which MV Cable test you are referring too. That being said, IEEE 400 covers testing of MV above 5kV Cables. Just to name a few:

    IEEE 400 Guide for Field Testing and Evaluation of the Insulation of Shielded Power Cable Systems Rated 5 kV and Above
    IEEE 400.1 Guide for Field Testing of Laminated Dielectric, Shielded AC Power Cable Systems Rated 5 kV to 500 kV Using High Voltage Direct Current (HVDC)
    IEEE 400.2 Guide for Field Testing of Shielded Power Cable Systems Using VLF
    IEEE 400.3 Guide for Partial Discharge Testing of Shielded Power Cable Systems in a Field Environment
    IEEE 400.4 Guide for Field Testing of Shielded Power Cable Systems Rated 5 kV and Above with Damped Alternating Current (DAC) Voltage

Subscribe

Share this thread

Related Topics

  1. Correct test voltage for 5KV cable?
    By lfmontoyas in forum NETA Level 3 Exam
    Replies: 9
    Last Post: March 29, 2020, 11:45 AM
  2. How many conductors in RS-485 cable?
    By tylerfini3 in forum NETA Level 3 Exam
    Replies: 2
    Last Post: February 23, 2020, 08:08 AM
  3. Minimum discharge time at end of cable test
    By Cldpmu in forum NETA Level 2 Exam
    Replies: 3
    Last Post: December 21, 2018, 10:08 PM
  4. Practice Test Question: MC Cable Bend Radius
    By EricGoetz92 in forum NETA Level 3 Exam
    Replies: 2
    Last Post: June 13, 2018, 02:58 PM
  5. NETA II test question (cable area)
    By dbryce89 in forum NETA Level 2 Exam
    Replies: 1
    Last Post: February 15, 2018, 10:52 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net