We recently had an incident at my shop where a technician was shocked while taking an oil sample from a pad-mount transformer. From what I understand, he was leaning on the enclosure when he grabbed the sample valve and there was a difference in potential between the two points which caused him to get hit.
Sounds like the voltage difference was pretty high considering he had trouble breaking free, this typically happens when you get above the 120V range. Based on this information my first guess is that the enclosure was not properly grounded.
Just wanted to share this incident in case others had similar stories. I remember seeing a question in NETA world a while back that addressed an issue like this, it wen't along the lines of "what's the first thing you do when you walk up to inspect an energized transformer?" The answer was inspect the tank ground.
Seems like this is one of those things that is hard to prevent, even if you inspect the ground and it looks good, you don't know what the condition is underground. Obviously the safest thing to do is not sample from an energized transformer but we all know this isn't always possible.
What kind of checks do you guys do in the field to prevent such an issue? It's not very practical to do a 3-point test on every transformer you want to sample but one solution would be to carry a ground rod with a lead that you can drive into the ground and connect to the tank while you sample.
I'd love to get any other stories or opinions from the community on this one. If I get any more details about the incident I'll be sure to share them here.