Follow Us
Results 1 to 2 of 2

What is the combined load in KVA & PF?

    #1
  1. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    What is the combined load in KVA & PF?

    Two loads are connected to the same source. Load 1: 1250KVA @ 0.85PF. Load 2: 600KW, 300KVAR. What is the combined load in KVA & PF?

    Another user posted 1825.8kVA @ 0.91 PF in a different thread and I couldn't come up with this answer. Here is what I did:

    Find combined PF:

    1.) Using individual PF, calculate KW and KVAR of each load
    2.) Add KW of each load to find combined KW
    3.) Add KVAR of each load to find combined KVAR
    4.) Combined PF is calculated as:
    4a.) Tan0 = Combined KVAR / Combined KW
    4b.) Combined PF = Cos (TanInv0)

    1a) 1,062.5kW, 658.478kVAR = 1,250,000VA @ 0.85 PF
    1b) 600kW, 300kVAR = 670,820VA @ 0.8944 PF
    2.) Combined kW = 1,662,500 W
    3.) Combined kVAR = 958,478 VAR
    4a.) Tan0 = 958,478 / 1,662,500 = 0.5765281
    4b.) Cos(TanInv0.5765281) = Cos(29.9646573) = 0.8663

    Find kVA using combined values and A^2 + B^2 = C^2, then sqrt(C^2):

    1.) 1662.500^2 = 2763906.25
    2.) 958.478^2 = 918680.076484
    3.) 2763906.25 + 918680.076484 = 3682586.326484
    4.) sqrt(3682586.326484) = 1,919.006

    Result: 1,919kVA @ 0.87PF

    Can someone check my work and let me know if I'm doing something wrong? I was able to verify my combined values using this calculator: https://www.omnicalculator.com/physics/power-factor

    Original thread: https://testguy.net/threads/5088-NET...estions-1-2017

  2. #2
  3. driftmy240 is offline Junior Member Pro Subscriber
    Join Date
    Oct 2017
    Posts
    1
    Reputation
    Quote Originally Posted by SecondGen View Post
    Two loads are connected to the same source. Load 1: 1250KVA @ 0.85PF. Load 2: 600KW, 300KVAR. What is the combined load in KVA & PF?

    Another user posted 1825.8kVA @ 0.91 PF in a different thread and I couldn't come up with this answer. Here is what I did:

    Find combined PF:

    1.) Using individual PF, calculate KW and KVAR of each load
    2.) Add KW of each load to find combined KW
    3.) Add KVAR of each load to find combined KVAR
    4.) Combined PF is calculated as:
    4a.) Tan0 = Combined KVAR / Combined KW
    4b.) Combined PF = Cos (TanInv0)

    1a) 1,062.5kW, 658.478kVAR = 1,250,000VA @ 0.85 PF
    1b) 600kW, 300kVAR = 670,820VA @ 0.8944 PF
    2.) Combined kW = 1,662,500 W
    3.) Combined kVAR = 958,478 VAR
    4a.) Tan0 = 958,478 / 1,662,500 = 0.5765281
    4b.) Cos(TanInv0.5765281) = Cos(29.9646573) = 0.8663

    Find kVA using combined values and A^2 + B^2 = C^2, then sqrt(C^2):

    1.) 1662.500^2 = 2763906.25
    2.) 958.478^2 = 918680.076484
    3.) 2763906.25 + 918680.076484 = 3682586.326484
    4.) sqrt(3682586.326484) = 1,919.006

    Result: 1,919kVA @ 0.87PF

    Can someone check my work and let me know if I'm doing something wrong? I was able to verify my combined values using this calculator: https://www.omnicalculator.com/physics/power-factor

    Original thread: https://testguy.net/threads/5088-NET...estions-1-2017
    I calculated it two different ways and got the same answer you did.
    Load 1 + Load 2 = 1,919kVA, PF=0.87

Subscribe

Share this thread

Related Topics

  1. Switching under full load
    By TrapFlyVenus in forum Safety and Arc Flash Talk
    Replies: 5
    Last Post: March 19, 2022, 03:52 PM
  2. Full-load current for single-phase AC motor
    By test11 in forum NETA Level 2 Exam
    Replies: 1
    Last Post: June 17, 2020, 11:45 AM
  3. Load tap changer location
    By Achandler in forum Electrical Testing Talk
    Replies: 2
    Last Post: May 20, 2020, 09:05 AM
  4. Replies: 0
    Last Post: January 16, 2020, 02:18 PM
  5. Load currents in an alternator
    By JeremyBrown87 in forum NETA Level 3 Exam
    Replies: 3
    Last Post: March 29, 2019, 11:57 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net