    Circuit Breaker Primary Injection Excel Sheet

    Hi guys,
    I hope you all okay. I just wanted to ask do you have any excel sheet to use in Primary Injection test to see the Long time, short time values? If you have i would be glad if you share.
    Stay safe.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by changeabilities View Post
    Hi guys,
    I hope you all okay. I just wanted to ask do you have any excel sheet to use in Primary Injection test to see the Long time, short time values? If you have i would be glad if you share.
    Stay safe.
    These values will be dependent on the specific type of trip unit you are testing but as a general reference I would recommend downloading the Utility Relay AC Pro Instruction Book for generic equations. I've included screenshots of the LT and ST formula along with a link to the original manual below, check out page 20.

    Click image for larger version. 

Name:	ac-pro-lt-st-formulas.png 
Views:	4 
Size:	158.1 KB 
ID:	459

    http://www.utilityrelay.com/PDFs/Pro...ion_Manual.pdf

  4. #3
  5. Join Date
    Jun 2018
    Posts
    23
    Reputation
    Quote Originally Posted by SecondGen View Post
    These values will be dependent on the specific type of trip unit you are testing but as a general reference I would recommend downloading the Utility Relay AC Pro Instruction Book for generic equations. I've included screenshots of the LT and ST formula along with a link to the original manual below, check out page 20.

    Click image for larger version. 

Name:	ac-pro-lt-st-formulas.png 
Views:	4 
Size:	158.1 KB 
ID:	459

    http://www.utilityrelay.com/PDFs/Pro...ion_Manual.pdf
    Thank you so much for your response.

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by changeabilities View Post
    Thank you so much for your response.
    No problem, I'd also recommend checking out the table on page 18 it will give you some expected trip times for the LT function along with allowable tolerance for various bands and test currents. Again, this may be different depending on the specific trip unit but it gives you a general idea.

    Click image for larger version. 

Name:	ac-pro-lt-table-ex.png 
Views:	66 
Size:	22.2 KB 
ID:	460

Subscribe

Share this thread

Related Topics

  1. Primary Injection Minimum Breaker Size As Per NETA
    By dnigra in forum Electrical Testing Talk
    Replies: 6
    Last Post: January 27, 2021, 02:50 PM
  2. Circuit Breaker Control Circuits Quick Reference Sheet (Time Saver)
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: September 29, 2018, 05:01 PM
  3. Primary Current Injection Test
    By changeabilities in forum Electrical Testing Talk
    Replies: 4
    Last Post: August 12, 2018, 08:17 AM
  4. Primary current injection 138kV breaker with bushing CT's
    By david2458 in forum Electrical Testing Talk
    Replies: 1
    Last Post: April 12, 2018, 05:27 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net