Originally Posted by
zi_zhang
Hi there I am new to this so please excuse me if I post this on the wrong place. Anyway took the level 2 practice Exam on test guy and the one of the question ask:
"A three phase transformer with a 13,200 volt delta connected primary and a 480Y/277V wye connected secondary is turns ratio tested, what ratio value would you expect to measure?"
So base on the question since the primary is Delta connected that mean 13200v is phase to phase voltage. therefore 480v is also phase to phase voltage on the secondary side. I did the math (13200/480) it give me a TTR of 27.5. so why did the test guy told me i got the wrong answer. i mean i never seen a 13200 phase to line voltage before out in the real world so what am I doing wrong. Please help, thanks in advance.