I have a few questions for anyone who does a lot of current transformer testing. We use Vanguard's EZCT-2000C Plus for testing CT's.
NETA ATS-2017 Current Transformers 7.10.1
4. Ratio errors shall be in accordance with IEEE C57.13
- From what I have been able to find in that standard (2008) :
- Relay Class C Classification= 3% error at rated current and 10% at 20 times rated current.
- Metering Class will be given an accuracy rating for each standard burden, i.e. 0.3 B-0.1 (0.3% accuracy)
* What do most of you use for % error?
5. Excitation results shall match the curve supplied by the manufacturer or be in accordance with IEEE C57.13.1
- From that standard:
"Any substantial deviation of the excitation curve for the CT under test from curves of similar CT's or
manufacturer's data shall be investigated."
* There isn't really a definitive percentage or other quantity to describe "substantial". Anyone have any
information on this?
* How many of you actually find the excitation curves?
Any input on this subject would be greatly appreciated.