We tested some bar type current transformers in a piece of MV switchgear recently that required us to remove the tape from the 15kV cable terminations. What is the reason for taping these terminations and what can happen if they aren't taped? There were also some terminations in this piece of gear that weren't taped and there didn't seem to be any signs of damage.
The piece of switchgear we were working on was an Eaton VacClad-W. The manual for this equipment list "Metal-clad switchgear field taping procedure" in the contents. Goes on to say:
- "
For incoming or outgoing terminations, these approved materials and not supplied by Eaton and must be
obtained and installed by others as identified in the definitions."
- "
Failure to install field insulation where necessary in accordance with these instructions will compromise the
electrical ratings of the switchgear assembly. Install field insulation to maintain the electrical ratings."
Powell Article:
https://www.powellind.com/sites/down...onnections.pdf
Anyone have experience with this kind of termination?