    Does NETA Specify 300% for Breaker Testing?

    Is there a neta spec for what current multiple to use to test circuit breaker functions? I was told to only use 300% the plug rating for a long time trip but 600% makes much more sense considering most delays are based off that.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by TrapFlyVenus View Post
    Is there a neta spec for what current multiple to use to test circuit breaker functions? I was told to only use 300% the plug rating for a long time trip but 600% makes much more sense considering most delays are based off that.
    NETA ATS 7.6.1.1.B.5 Determine long-time pickup and delay by primary current injection.

    NETA ATS 7.6.1.1.D.5 Long-time pickup values shall be as specified, and the trip characteristic shall not exceed manufacturer’s published time-current characteristic tolerance band, including adjustment
    factors. If manufacturer’s curves are not available, trip times shall not exceed the value
    shown in Table 100.7.

    NEMA AB4 6.5.4.2 With the test circuit breaker closed, energize the test circuit and quickly adjust the transformer to the required 300% test current.

    So, NETA does not require you test at 300%, and I have found myself testing at lower values multiple times before due to test equipment limitations. Any current multiple is allowed, as long as it falls within the manufacturer specifications. That being said, I would never test at 6x, simply cause it causes more problems in the long run, especially with larger sized breakers and bus/cable limitations. NEMA AB4 also provides tables for suggested bussing and cable sizes.
    If you have a breaker fail, and send it back to the customer, they may find the OEM arguing that you did not test per NEMA AB4 (NEMA = National Electrical Manufacturer's Association). Thus, it is recommended to test per NEMA AB4 since it is the standard used for testing per the Manufacturer, and they call for testing LT at 300%.

Subscribe

Share this thread

Related Topics

  1. Primary Injection Minimum Breaker Size As Per NETA
    By dnigra in forum Electrical Testing Talk
    Replies: 6
    Last Post: January 27, 2021, 02:50 PM
  2. Free courses on the basics of breaker testing?
    By tylerfini3 in forum Electrical Testing Talk
    Replies: 6
    Last Post: February 2, 2020, 11:47 AM
  3. How do you Primary inject the neutral of a 4 pole circuit breaker?
    By TrapFlyVenus in forum Electrical Testing Talk
    Replies: 3
    Last Post: January 12, 2020, 01:23 PM
  4. Circuit Breaker Grounding Cart Testing
    By roberts311 in forum Electrical Testing Talk
    Replies: 2
    Last Post: May 16, 2018, 02:06 AM
  5. training for low voltage circuit breaker testing
    By Tdreissig0505 in forum Electrical Testing Talk
    Replies: 2
    Last Post: December 7, 2017, 11:27 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net