    Percentage Differential Mismatch

    Calculate the percentage differential mismatch for an electromechanical relay protecting a 138kV-69kV Delta-Wye 50MVA Transformer with 250:5 CTs on the primary and 500:5 CTs on the secondary, with CT ratio taps on the relay set to 5A on the high side and 9A on the low side.

    I need help with this problem, the answer is supposedly 3.78%. Thanks.

  2. #2
  3. Erased is offline Junior Member
    Join Date
    Oct 2020
    Posts
    2
    Reputation
    Quote Originally Posted by Uguessus View Post
    Calculate the percentage differential mismatch for an electromechanical relay protecting a 138kV-69kV Delta-Wye 50MVA Transformer with 250:5 CTs on the primary and 500:5 CTs on the secondary, with CT ratio taps on the relay set to 5A on the high side and 9A on the low side.

    I need help with this problem, the answer is supposedly 3.78%. Thanks.
    Now, I got a slightly different answer, so someone correct me if I'm mistaken.

    First calculate HV currents.

    Primary:
    50000000/sqrt(3)*138000 = 209.18

    Secondary:
    50000000/sqrt(3)*69000 = 418.37

    Now calculate CT currents. An electromechanical scheme on a Delta-Wye will have Wye-Delta CT's to account for the phase shift. Delta CT current must be multiplied by sqrt(3).

    Primary - Wye CT:
    209.18/50 = 4.18

    Secondary - Delta CT:
    418.37/100 = 4.18
    4.18*sqrt(3) = 7.24

    Calculate the percent mismatch as follows: On two-winding transformers,
    determine the ratio of the two relay currents and the tap values selected. The
    difference between these ratios, divided by the smaller ratio, is the percent
    mismatch.

    ((4.18/5)-(7.24/9)) / (7.24/9) = 0.0392

    3.92% with rounding errors.

    Looks like your answer came from incorrectly dividing by the larger ratio.

    (4.18/5)-(7.24/9) / (4.18/5) = 0.0377

    3.77% with rounding errors.

  4. #3
  5. Uguessus is offline Junior Member Pro Subscriber
    Join Date
    Dec 2019
    Location
    Signal Hill, CA
    Posts
    5
    Reputation
    This is awesome! Thanks a lot, Erased.

  6. #4
  7. rjhrick03 is offline Junior Member Pro Subscriber
    Join Date
    Apr 2016
    Posts
    1
    Reputation

    Still the "wrong" answer in practice test

    If the below explanation is correct, the practice test question is still incorrect as of Feb 2021. Just want to confirm...the correct answer is 3.92%?

    Quote Originally Posted by Erased View Post
    Now, I got a slightly different answer, so someone correct me if I'm mistaken.

    First calculate HV currents.

    Primary:
    50000000/sqrt(3)*138000 = 209.18

    Secondary:
    50000000/sqrt(3)*69000 = 418.37

    Now calculate CT currents. An electromechanical scheme on a Delta-Wye will have Wye-Delta CT's to account for the phase shift. Delta CT current must be multiplied by sqrt(3).

    Primary - Wye CT:
    209.18/50 = 4.18

    Secondary - Delta CT:
    418.37/100 = 4.18
    4.18*sqrt(3) = 7.24

    Calculate the percent mismatch as follows: On two-winding transformers,
    determine the ratio of the two relay currents and the tap values selected. The
    difference between these ratios, divided by the smaller ratio, is the percent
    mismatch.

    ((4.18/5)-(7.24/9)) / (7.24/9) = 0.0392

    3.92% with rounding errors.

    Looks like your answer came from incorrectly dividing by the larger ratio.

    (4.18/5)-(7.24/9) / (4.18/5) = 0.0377

    3.77% with rounding errors.

  8. #5
  9. Join Date
    Jan 2021
    Location
    UK
    Posts
    5
    Reputation
    https://cms-cdn.selinc.com/assets/Li...0190509-181852
    All information here related to the topic kindly visit this site and my collection its very helpful to you.Thank You!

Subscribe

Share this thread

Related Topics

  1. Differential Slope 1 and 2
    By Js20981 in forum P&C / Relay Testing Talk
    Replies: 1
    Last Post: February 8, 2021, 04:36 PM
  2. Replies: 3
    Last Post: April 6, 2020, 08:54 PM
  3. Replies: 3
    Last Post: January 13, 2016, 01:39 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net