Good day everyone. I was task to check a 12kV 800A vacuum circuit breaker for 4.16kV application. As part of pre-requisite prior to accepting the item as spare, we conducted insulation and contact resistance. Insulation resistance is acceptable. What concerns me is the big difference in reading when we conduct the contact test.
L1-L1 = 56.4 micro-ohms
L2-L2 = 34.7 micro-ohms
L3-L3 = 242.0 micro-ohms
The 3rd contact is so high compared to the other two (2). I read somewhere in this forum that we can not just take a 10A injection test as basis for judging if the contact resistance is good or bad. By the way, I use a Megger DLRO10HD with 10A 2.5 milliohms setting.
I manage to secure a copy of Factory Acceptance Test Report of similar VCB and it says the acceptance criteria is 0-90 micro-ohms. I don't know how they conduct their test at the factory but I think they use higher amp.
For me personally I will not accept it and something must be done. Badly need some technical and legal (if there is
) feedbacks from you guys. I already inform our supplier and waiting for their feedback.