SecondGen
Setting up the test set properly is arguably the hardest part when it comes to primary-injection testing. First off you need a really good power source, so something like 100A of 480V. Then you need a good collection of copper bus, test cables, and c-clamps so you can connect to the breaker you are testing. Most drawout breakers can be connected directly to the stabs, but just about every insulated and molded case breaker is going to require you to get creative.
One trick I always like to use is short all phases on the load side of the breaker, that way you only move your line side lead when switching phases.
Once you have the breaker securely on the test set and a good power source, the testing will go smooth. If you want to keep the current level low and specs allow for it you can dial settings down for your timing tests at 3x 1.5x and instantaneous. I generally don't like going over 15kA so I will dial down whenever possible. Also you will get an arm workout from charging and closing the breakers all day, best to hookup control power whenever possible.
It's good to have the secondary set for the trip unit you are working with so that you can power the unit and defeat ground fault, if enabled. Some breakers can be defeated with a jumper, otherwise you will need to wire 2 phases in series.