What rating lightning arrestor would be suitable for a 13800/7900V system? Your Answer: 15kV Correct Answer: 10kV There are two different ratings for 13.8 kV. How do you determine from this question which one they are looking for?
Originally Posted by breny426 What rating lightning arrestor would be suitable for a 13800/7900V system? Your Answer: 15kV Correct Answer: 10kV There are two different ratings for 13.8 kV. How do you determine from this question which one they are looking for? The question includes line to ground voltage levels of 7900v. This means you wouldn't choose the delta or ungrounded rated MCOV arrestor ratings.