    Phase Failure Relay Test Procedure

    Does anyone have a procedure to test a PFR? The use is for a 480V pump motor, and I can only think of applying voltage to all 3 phases and then drop a phase to see if it works or reverse the rotation. Thanks in advance.

  2. #2
  3. Join Date
    Dec 2017
    Posts
    32
    Reputation

    undervoltage/loss of phase

    Quote Originally Posted by Fieldtech View Post
    Does anyone have a procedure to test a PFR? The use is for a 480V pump motor, and I can only think of applying voltage to all 3 phases and then drop a phase to see if it works or reverse the rotation. Thanks in advance.
    Isn't it just like a basler BE3-27 ? I think you are correct! just make sure how many legs and what voltage you are supposed to see (Delta or Wye) L-L voltage or L-G.

    The relay also should have contacts for NO and/or NC.

Subscribe

Share this thread

Related Topics

  1. Why is the Network Protector phase relay tested at 60° angle?
    By StoneyJ180 in forum P&C / Relay Testing Talk
    Replies: 2
    Last Post: August 21, 2018, 01:36 PM
  2. Transformer vector group test procedure
    By YugiGrobler in forum Electrical Testing Talk
    Replies: 0
    Last Post: November 27, 2017, 07:04 PM
  3. Phase Sequence Relay Testing (Tengen XJ3-G)
    By lnides in forum P&C / Relay Testing Talk
    Replies: 3
    Last Post: May 30, 2016, 03:25 PM
  4. Replies: 3
    Last Post: January 13, 2016, 01:39 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net