    Holes in 22KV Busbar

    Hi there,
    I hope you all are doing well. I need a suggestion, that we have a 22KV busbar and already provided holes are somehow out means we can't use them for fastening our busbar with the bus support insulator. Can we make new holes? while leaving the old ones open. I am curious that how new holes will affect the mechanical strength and other characteristics of the busbar.

  2. #2
  3. RabbleRabble is offline Member Pro Subscriber
    Join Date
    Apr 2020
    Posts
    28
    Reputation
    Quote Originally Posted by Waqas2121 View Post
    Hi there,
    I hope you all are doing well. I need a suggestion, that we have a 22KV busbar and already provided holes are somehow out means we can't use them for fastening our busbar with the bus support insulator. Can we make new holes? while leaving the old ones open. I am curious that how new holes will affect the mechanical strength and other characteristics of the busbar.
    You will reduce the ampacity as you reduce the cross sectional area.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Waqas2121 View Post
    Hi there,
    I hope you all are doing well. I need a suggestion, that we have a 22KV busbar and already provided holes are somehow out means we can't use them for fastening our busbar with the bus support insulator. Can we make new holes? while leaving the old ones open. I am curious that how new holes will affect the mechanical strength and other characteristics of the busbar.
    As others have stated, you will lower the ampacity of the bus bar by making additional holes. With that said, depending on how many holes and the size, you might be able to modify without greatly affecting the bus bar. It's hard to say without detailed specifications.