    Grounding cables not under test

    When testing A-phase of a three-phase cable, B and C Phases are grounded because:

    Any ideas, all i know is that "It may induce a high voltage into them" is not the right answer

  2. #2
  3. gchoquette is offline Junior Member Pro Subscriber
    Join Date
    Mar 2019
    Posts
    22
    Reputation
    Quote Originally Posted by epenland View Post
    Any ideas, all i know is that "It may induce a high voltage into them" is not the right answer
    By grounding the other two, you will immediately find out if there is a phase-phase short. Specifically, it will allow you to see if phase A is shorted to phase B or phase C.
    Last edited by gchoquette; February 11, 2021 at 06:30 PM. Reason: Clarification