    Quote Originally Posted by bec51392 View Post
    Applying a solidly grounded wire immediately after performing a high-potential test:
    Your Answer: Will ensure immediate personally safety.
    Correct Answer: May damage the insulation under test.

    I cant find anything that supports this. Everything I read says ground it after....
    You guys have already found the standards but I'll just add, I've seen nasty cable discharges back in the old days of DC hipoting. Terminations can easily be damaged if you don't give it some time (4x test period was the rule of thumb) or use a discharge stick. Some guys just attached a rubber bungie cord to a ground, they have about 8 ohms resistance.

  2. #12
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by SecondGen View Post
    You guys have already found the standards but I'll just add, I've seen nasty cable discharges back in the old days of DC hipoting. Terminations can easily be damaged if you don't give it some time (4x test period was the rule of thumb) or use a discharge stick. Some guys just attached a rubber bungie cord to a ground, they have about 8 ohms resistance.
    After discharging with a homemade ground stick, I would apply electric fence wire to the terminals and ground and leave for the electricians to remove. I've seen cables (~2000ft long or more) build a charge after 24 hrs grounded.

  4. #13
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    After discharging with a homemade ground stick, I would apply electric fence wire to the terminals and ground and leave for the electricians to remove. I've seen cables (~2000ft long or more) build a charge after 24 hrs grounded.
    Another great point, can also confirm long cable runs will rebuild a charge. I've even seen this happen on low voltage cable too but not as severe as MV. It's a good idea to leave cables grounded with some bare wire for the next guy, if possible.

    When you don't have wire, you can even just lay the exposed conductor against the equipment enclosure or ground bus, anything helps. Nobody wants to be responsible for having someone get bit.

  6. #14
  7. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by epenland View Post
    Applying a solidly grounded wire immediately after performing a high-potential test:
    it cause damage to the cable you just test

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. VLF vs AC HiPot
    By Kalbi_Rob in forum Electrical Testing Talk
    Replies: 13
    Last Post: May 4, 2021, 05:44 AM
  2. Grounding cables not under test
    By epenland in forum NETA Level 2 Exam
    Replies: 1
    Last Post: February 11, 2021, 01:58 PM
  3. 15kv vacuum breaker maintenance hipot test voltage
    By Fieldtech in forum Electrical Testing Talk
    Replies: 7
    Last Post: October 8, 2020, 12:13 PM
  4. Replies: 2
    Last Post: January 20, 2020, 09:35 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net