    Breaker Contact Resistance by Type

    Which of these contact resistance (in micro-ohms) readings are passing?

    A: 3200A Masterpact Breaker: A - 1252, B - 1300, C - 1171
    B: 400A Eaton Molded Case Breaker: A - 850, B - 772, C - 813
    C: 1200A VCP-W Breaker: A - 150, B - 151, C - 145
    D: 15KV GE OCB Breaker: A - 175, B - 300, C - 425

    What do you guys think? everyting seems high to me

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by adamwilson View Post
    Which of these contact resistance (in micro-ohms) readings are passing?

    A: 3200A Masterpact Breaker: A - 1252, B - 1300, C - 1171
    B: 400A Eaton Molded Case Breaker: A - 850, B - 772, C - 813
    C: 1200A VCP-W Breaker: A - 150, B - 151, C - 145
    D: 15KV GE OCB Breaker: A - 175, B - 300, C - 425

    What do you guys think? everyting seems high to me
    Per NETA, there cannot be 50% difference between readings, thus you take the lowest reading and multiply by 1.5, and the highest reading cannot exceed that value.

    D is failing since 175*1.5=262.5, and both b and c are higher than 262.5

    As a general look, A, C and D look abnormally high with regards to expected readings, but in spec per NETA.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Per NETA, there cannot be 50% difference between readings, thus you take the lowest reading and multiply by 1.5, and the highest reading cannot exceed that value.

    D is failing since 175*1.5=262.5, and both b and c are higher than 262.5

    As a general look, A, C and D look abnormally high with regards to expected readings, but in spec per NETA.
    Agree that D looks pretty bad and the others are really high. Just knowing from experience that those specific breakers are way out of normal range, except maybe the molded case. I'd probably write up A and C as well in the real world.

    Question could probably use some language that specifies NETA. If I wasn't going off NETA, all would probably fail by my standards, except the molded case, making my answer B.

  6. #4
  7. Join Date
    Apr 2021
    Posts
    32
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Per NETA, there cannot be 50% difference between readings, thus you take the lowest reading and multiply by 1.5, and the highest reading cannot exceed that value.

    D is failing since 175*1.5=262.5, and both b and c are higher than 262.5

    As a general look, A, C and D look abnormally high with regards to expected readings, but in spec per NETA.
    Thank you for the informative reply, I feel like I have come across this type of questions before, and now I know what to look for.

  8. #5
  9. TestingProToBe is offline Junior Member Pro Subscriber
    Join Date
    Dec 2017
    Posts
    14
    Reputation
    Quote Originally Posted by adamwilson View Post
    Which of these contact resistance (in micro-ohms) readings are passing?

    A: 3200A Masterpact Breaker: A - 1252, B - 1300, C - 1171
    B: 400A Eaton Molded Case Breaker: A - 850, B - 772, C - 813
    C: 1200A VCP-W Breaker: A - 150, B - 151, C - 145
    D: 15KV GE OCB Breaker: A - 175, B - 300, C - 425

    What do you guys think? everyting seems high to me
    I would have to agree with you. All of these results do seem high. However if I were testing these breakers and I knew they all had some years of service on them then I would probably only be concerned with the masterpact, should never be that high, and the 15kv breaker. I find medium voltage breakers usually have pretty great ductor readings, then again I test more low voltage breakers. And as far as the molded case goes- I’d try exercising the breaker a few times, see if it gets better and if it doesn’t just keep an eye on it. No need to junk it just yet.

  10. #6
  11. LarryJ is offline Junior Member Pro Subscriber
    Join Date
    Jan 2018
    Location
    Pittsburgh
    Posts
    4
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Per NETA, there cannot be 50% difference between readings, thus you take the lowest reading and multiply by 1.5, and the highest reading cannot exceed that value.

    D is failing since 175*1.5=262.5, and both b and c are higher than 262.5

    As a general look, A, C and D look abnormally high with regards to expected readings, but in spec per NETA.
    Where can I find this in the NETA Handbook

  12. #7
  13. rofo42 is offline Seasoned Member
    Join Date
    Apr 2018
    Posts
    65
    Reputation
    Quote Originally Posted by LarryJ View Post
    Where can I find this in the NETA Handbook
    Page 72 of the 2019 MTS

  14. #8
  15. LarryJ is offline Junior Member Pro Subscriber
    Join Date
    Jan 2018
    Location
    Pittsburgh
    Posts
    4
    Reputation

    Thanks

    Quote Originally Posted by rofo42 View Post
    Page 72 of the 2019 MTS

  16. #9
  17. Join Date
    Feb 2015
    Location
    Red Oak TX
    Posts
    26
    Reputation
    Quote Originally Posted by adamwilson View Post
    Which of these contact resistance (in micro-ohms) readings are passing?

    A: 3200A Masterpact Breaker: A - 1252, B - 1300, C - 1171
    B: 400A Eaton Molded Case Breaker: A - 850, B - 772, C - 813
    C: 1200A VCP-W Breaker: A - 150, B - 151, C - 145
    D: 15KV GE OCB Breaker: A - 175, B - 300, C - 425

    What do you guys think? everyting seems high to me

    I would say C
    It is within the 150% acceptable range.

    A is very high for a 3200 amp breaker. B may be OK (but C is better), D is not within 150%.

    The 400 amp breaker is 1/3 the size of the 1200 amp breaker, but the resistances are 5 times the amount. If the 400 amp breaker was closer to 450 per phase, I would say that would be passing for the 400 amp breaker.

Subscribe

Share this thread

Related Topics

  1. Contact resistance tester doesn't display any reading
    By lnides in forum Electrical Testing Talk
    Replies: 12
    Last Post: December 21, 2020, 01:32 PM
  2. Replies: 8
    Last Post: August 16, 2020, 02:49 PM
  3. Expected contact resistance measurement based on breaker frame size
    By SecondGen in forum Electrical Testing Talk
    Replies: 6
    Last Post: July 11, 2020, 03:01 PM
  4. Contact resistance test producing CT secondary current
    By alexlounsbury in forum P&C / Relay Testing Talk
    Replies: 9
    Last Post: November 20, 2019, 06:21 PM
  5. VCB Contact Resistance
    By shamimkhan in forum Electrical Testing Talk
    Replies: 1
    Last Post: December 8, 2017, 10:36 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net