Originally Posted by
mike01
Thanks for the information appreciated, the manufacturer did provide this I found interesting as well "wax on the breaker contacts put on for shipping purposes that would also affect the readings."
The circuit breaker is installed in a panelboard [main breaker / currently not-energized] there are insulation resistance table as you indicated with insulation resistance from "Pole to Pole", Pole to Frame" and "Line to Load" all readings are exactly the same in every cell of the table (2,000 Mohm) corrected to 20 degree C with a multiplier of 1.056. is it odd that every value is exactly 2,000 or is this just where meters top out at? The pole resistance readings is checked in Micro-Ohms with Pole 1=388, Pole 2=638 and Pole 3=399. I am not sure what the "pole resistance" method was / where the connections were made.
The phase to handle instead of ground is also interesting something I never thought of. I was not there when the testing was done so have no idea the procedure used or how it was done. I assume they removed the breaker and "bench tested" it does not appear to have been done that way, also it appears no injection testing was done that whole section of the form is blank. THANKS AGAIN.